    Coalescer Element



    Hi

    I changed today coalescer element to sab 163 hr compressor. I took pictures before and after change.

    Can you see difference between new and old?


    HPIM3899 (800x600).jpgHPIM3900 (800x600).jpg



    I hope that this helps for "little" oil carry-over problem because it was quite far from nominal



  2. #2
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Coalescer Element

    I`ve seen that many a time. The best was when it took two of use all morning to hammer the element out.

  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Coalescer Element

    Quote Originally Posted by Teuria View Post
    Hi

    I changed today coalescer element to sab 163 hr compressor. I took pictures before and after change.

    Can you see difference between new and old?


    HPIM3899 (800x600).jpgHPIM3900 (800x600).jpg



    I hope that this helps for "little" oil carry-over problem because it was quite far from nominal
    Yes, I can see the difference
    To make progress is never good enough, I want to do better and better and better

  4. #4
    Join Date
    Jun 2008
    Location
    Finland
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: Coalescer Element

    Quote Originally Posted by glenn1340 View Post
    I`ve seen that many a time. The best was when it took two of use all morning to hammer the element out.
    Can you explain why it goes like this? Refrigerant gas goes inside the filter, right?
    So why it doesn't explode outward?

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Coalescer Element

    Respectfully suggest that the compressor is loading too fast and discharge pressure/ flow rate creates a high differential across coalesar element. Slow the compressor capacity load rate.
    The flow is outside to inside imploding the screen element.

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Coalescer Element

    Quote Originally Posted by Magoo View Post
    Respectfully suggest that the compressor is loading too fast and discharge pressure/ flow rate creates a high differential across coalesar element. Slow the compressor capacity load rate.
    The flow is outside to inside imploding the screen element.
    No, if I understood what you mean the flow (vapour + residual oil) is inside to outside and not outside to inside.
    To make progress is never good enough, I want to do better and better and better