Thread: Frequent Failures
-
03-01-2006, 09:37 PM #1
Frequent Failures
Hi Everyone
Anyone got any bright ideas?
Recently I visited a site complaining that a trane chiller CVGF 75O had frequent failures. Diagnostic code starter not in transition. B4 they called me up they had already informed trane organization. But trane personnel did not rectify the problem. They concluded that the starter was faulty and need to be replaced. The customer was not happy with the reply.
For everyones info, total numbers of chillers 4 nos including the said chillers. Other chillers are working fine.
These are the attempted matters,
1. Starter module interchange between chillers.
2. All contactors service.
3. Contactor auxillary interchange betwn chillers.
4. Starter interchange betwn chillers.
5. Cables, wires and termination point all tightened.
6. Chiller mod, circuit mod interchange betwn chillers.
7. Simulation test carried outon other monitoring device and found in operating condition.
Chiller was running for 1 week and then problem came back again.
Any suggestion anyone????????
-
04-01-2006, 04:41 PM #2
Re: Frequent Failures
try thsi forum as it has a lot of trane guys
http://hvac-talk.com/vbb/forumdispla...=25&daysprune=
cheers
richard
p.s if you can't access it I can post for you
-
04-01-2006, 05:27 PM #3
Re: Frequent Failures
Originally Posted by Marc O'Brien
Do as Marc suggests he is spot on.... but keep the customer well informed as it may take weeks and many visits.:cool: Calvo :cool:
-
04-01-2006, 07:02 PM #4
Re: Frequent Failures
Originally Posted by Lazarus
cheers
richard
-
04-01-2006, 11:42 PM #5
Re: Frequent Failures
check the thermostat setting,differential pressure switch,ambient temperature switch,chilled water supply(Pressure),checked if the refrigerant is not less.You can check also if the compressor in not less compression,not lost compression.
-
05-01-2006, 12:20 AM #6
Re: Frequent Failures
Not familiure with this unit, but have you checked the grounding on the controls transformer and on the unit. Have you replaced the CT?
-
05-01-2006, 12:00 PM #7
Re: Frequent Failures
Hi Guys,
Thank you for all your comments, suggestions and help.
I've done most of you're all instruction. I'm still following up on the unit.
rb thanks for link.
-
05-01-2006, 07:37 PM #8
Re: Frequent Failures
LOL and i thought it was piles.............
:cool: Calvo :cool:
-
05-01-2006, 07:40 PM #9
Re: Frequent Failures
Originally Posted by Lazarus
piles of what though that's the question ??
cheers
richard
-
06-01-2006, 02:05 PM #10
Re: Frequent Failures
Have you tried interchange the changeover dely timer?
Running on Star Delta closed transition?
-
06-01-2006, 02:33 PM #11
Re: Frequent Failures
Hi Laz,
Piles normally protrude from the anus, very perculiar though??? I don't get your drift. Explain.
-
06-01-2006, 02:36 PM #12
Re: Frequent Failures
Hi Corfreth,
Presently the unit is running. No diagnostic failure whatsoever so far.
Thanks for the highlight.
-
06-01-2006, 11:22 PM #13
Re: Frequent Failures
Hi abdulazman,
Like a few other possibilities they can make you walk a little like youre avatar... :-):cool: Calvo :cool:
-
07-01-2006, 08:33 PM #14
Re: Frequent Failures
Hi Lazarus,
Unlikely the avatars' not afraid as those oppose gunslinger who carries gun with no bullet in it. With moustache thats similar to an undergrowth.
-
07-01-2006, 09:37 PM #15
Re: Frequent Failures
The avatars metaphysical prowess is understated but how can you tell his moustache is to small.... he's got all those bandages on!!
:cool: Calvo :cool:
-
08-01-2006, 07:24 AM #16
Re: Frequent Failures
Common sense,common sense
-
08-01-2006, 07:43 AM #17
Re: Frequent Failures
你们好啊
我是新来的!多照顾啊!
-
08-01-2006, 10:26 AM #18
Re: Frequent Failures
I incountered that nearly semilar trouble when I am in the middle east, is that unit with motor protector control or winding sensor thermistor? Check for MP.
rudimustardseed:) :) :)
-
08-01-2006, 11:25 AM #19
Re: Frequent Failures
I'd encountered semilar trouble when I am working in the middle east, is that unit with motor protector (MP) and there's a thermistor sensor in the winding. If does check the MP.
rudimustardseed:) :) :)
-
08-01-2006, 11:30 AM #20
Re: Frequent Failures
Hi rpb,
Herein are the pdf. file of the chiller.
Hey LJW,
What in god name are you muttering about, woh puh ker nerng????
-
08-01-2006, 02:20 PM #21
Re: Frequent Failures
I have the same problem encounterd when I am working in the meddle east, the TRANE centrifugal Chiller with 360 Tons the starter always cut off intermitently. Finally we got the problem from the motor winding thermistor problem with (MP) the motor protector.
rudimustardseed:) :) :)
-
08-01-2006, 07:40 PM #22
Re: Frequent Failures
By the way the chiller has already been in operation for sometime.
Thanks for the tip off mate.