    Frequent Failures



    Hi Everyone

    Anyone got any bright ideas?

    Recently I visited a site complaining that a trane chiller CVGF 75O had frequent failures. Diagnostic code starter not in transition. B4 they called me up they had already informed trane organization. But trane personnel did not rectify the problem. They concluded that the starter was faulty and need to be replaced. The customer was not happy with the reply.

    For everyones info, total numbers of chillers 4 nos including the said chillers. Other chillers are working fine.

    These are the attempted matters,

    1. Starter module interchange between chillers.
    2. All contactors service.
    3. Contactor auxillary interchange betwn chillers.
    4. Starter interchange betwn chillers.
    5. Cables, wires and termination point all tightened.
    6. Chiller mod, circuit mod interchange betwn chillers.
    7. Simulation test carried outon other monitoring device and found in operating condition.

    Chiller was running for 1 week and then problem came back again.

    Any suggestion anyone????????



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: Frequent Failures

    try thsi forum as it has a lot of trane guys

    http://hvac-talk.com/vbb/forumdispla...=25&daysprune=

    cheers

    richard

    p.s if you can't access it I can post for you

  3. #3
    Join Date
    Dec 2005
    Location
    Spain
    Posts
    61
    Rep Power
    19

    Re: Frequent Failures

    Quote Originally Posted by Marc O'Brien
    Intermittent faults, eeek. You have more than one chiller, have you swapped components to see whether the faults stay or follow?
    The real nightmare with intermittant faults are when you dont have any 'sister' machines there!!! i have spent many a happy hour swopping 'new' bits in and out. Or that 'loose' neutral wire in the back of the panel.
    Do as Marc suggests he is spot on.... but keep the customer well informed as it may take weeks and many visits.
    :cool: Calvo :cool:

  4. #4
    rbartlett's Avatar
    rbartlett Guest

    Re: Frequent Failures

    Quote Originally Posted by Lazarus
    Do as Marc suggests he is spot on....
    is he sh*ging you or what??

    cheers

    richard

  5. #5
    Join Date
    Aug 2005
    Location
    uk
    Posts
    45
    Rep Power
    0

    Re: Frequent Failures

    check the thermostat setting,differential pressure switch,ambient temperature switch,chilled water supply(Pressure),checked if the refrigerant is not less.You can check also if the compressor in not less compression,not lost compression.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Age
    59
    Posts
    25
    Rep Power
    0

    Re: Frequent Failures

    Not familiure with this unit, but have you checked the grounding on the controls transformer and on the unit. Have you replaced the CT?

  7. #7
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Frequent Failures

    Hi Guys,
    Thank you for all your comments, suggestions and help.
    I've done most of you're all instruction. I'm still following up on the unit.
    rb thanks for link.

  8. #8
    Join Date
    Dec 2005
    Location
    Spain
    Posts
    61
    Rep Power
    19

    Re: Frequent Failures

    LOL and i thought it was piles.............
    :cool: Calvo :cool:

  9. #9
    rbartlett's Avatar
    rbartlett Guest

    Re: Frequent Failures

    Quote Originally Posted by Lazarus
    LOL and i thought it was piles.............

    piles of what though that's the question ??

    cheers

    richard

  10. #10
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: Frequent Failures

    Have you tried interchange the changeover dely timer?
    Running on Star Delta closed transition?

  11. #11
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Frequent Failures

    Hi Laz,
    Piles normally protrude from the anus, very perculiar though??? I don't get your drift. Explain.

  12. #12
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Frequent Failures

    Hi Corfreth,
    Presently the unit is running. No diagnostic failure whatsoever so far.
    Thanks for the highlight.

  13. #13
    Join Date
    Dec 2005
    Location
    Spain
    Posts
    61
    Rep Power
    19

    Re: Frequent Failures

    Hi abdulazman,

    Like a few other possibilities they can make you walk a little like youre avatar... :-)
    :cool: Calvo :cool:

  14. #14
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Frequent Failures

    Hi Lazarus,
    Unlikely the avatars' not afraid as those oppose gunslinger who carries gun with no bullet in it. With moustache thats similar to an undergrowth.

  15. #15
    Join Date
    Dec 2005
    Location
    Spain
    Posts
    61
    Rep Power
    19

    Re: Frequent Failures

    The avatars metaphysical prowess is understated but how can you tell his moustache is to small.... he's got all those bandages on!!
    :cool: Calvo :cool:

  16. #16
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Frequent Failures

    Common sense,common sense

  17. #17
    Join Date
    Dec 2005
    Location
    baoding
    Posts
    7
    Rep Power
    0

    Re: Frequent Failures

    你们好啊
    我是新来的!多照顾啊!

  18. #18
    Join Date
    Jan 2006
    Location
    Newcastle, United Kingdom
    Posts
    30
    Rep Power
    0

    Re: Frequent Failures

    I incountered that nearly semilar trouble when I am in the middle east, is that unit with motor protector control or winding sensor thermistor? Check for MP.

    rudi
    mustardseed:) :) :)

  19. #19
    Join Date
    Jan 2006
    Location
    Newcastle, United Kingdom
    Posts
    30
    Rep Power
    0

    Re: Frequent Failures

    I'd encountered semilar trouble when I am working in the middle east, is that unit with motor protector (MP) and there's a thermistor sensor in the winding. If does check the MP.

    rudi
    mustardseed:) :) :)

  20. #20
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Frequent Failures

    Hi rpb,
    Herein are the pdf. file of the chiller.
    Hey LJW,
    What in god name are you muttering about, woh puh ker nerng????
    Attached Images Attached Images

  21. #21
    Join Date
    Jan 2006
    Location
    Newcastle, United Kingdom
    Posts
    30
    Rep Power
    0

    Re: Frequent Failures

    I have the same problem encounterd when I am working in the meddle east, the TRANE centrifugal Chiller with 360 Tons the starter always cut off intermitently. Finally we got the problem from the motor winding thermistor problem with (MP) the motor protector.

    rudi
    mustardseed:) :) :)

  22. #22
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Frequent Failures

    By the way the chiller has already been in operation for sometime.
    Thanks for the tip off mate.