29-09-2012, 07:23 AM #1
use of inverted P traps
Good evening to everyone. Iīm quite familiar with the use and purpose of oil traps at the bottom of suction line risers, and every other 5 meters, as you go up the riser. What I didnīt know was that an inverted P trap has to be installed at the TOP of the riser as well. I just saw pictures of this in a website that describes the correct installation of walk-ins. What would be the purpose of this inverted P trap? Keeping the oil and liquid refrigerant from flowing back into the evaporator by falling through the riser when the system is off?
-
29-09-2012, 08:40 AM #2
Re: use of inverted P traps
Hi coldseeker
In short yes, it stops oil draining back in the off cycle or reduced loading. Inverted P Traps are also used on some cooling towers to stop all the water in the pipe draining each time the pump shuts down.
-
29-09-2012, 08:44 PM #3
Re: use of inverted P traps
.
Yep.
As stated by Tesla the trap on the top of the riser
stops the oil from falling back down once it has reached
the top.
Regards
Rob.
.
-
01-10-2012, 06:11 AM #4
Re: use of inverted P traps
Good evening to all. I would like to add something I just learned in another forum: inverted P traps should be used at the top of individual suction risers whenever each riser belongs to evaporators which are being connected to a header or main suction line. In this way the oil going through the header does not fall into any of the evaporators during the off cycle. Actually, when I started this post, I was thinking on a single evaporator with a single suction riser. Thank you for your comments.
-
01-10-2012, 05:40 PM #5
Re: use of inverted P traps
.
Suction pipes should always go into the top of the header
and liquid pipes should always be conected to the bottom
of the header.
Regards
Rob
.