    use of inverted P traps



    Good evening to everyone. Iīm quite familiar with the use and purpose of oil traps at the bottom of suction line risers, and every other 5 meters, as you go up the riser. What I didnīt know was that an inverted P trap has to be installed at the TOP of the riser as well. I just saw pictures of this in a website that describes the correct installation of walk-ins. What would be the purpose of this inverted P trap? Keeping the oil and liquid refrigerant from flowing back into the evaporator by falling through the riser when the system is off?



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: use of inverted P traps

    Hi coldseeker
    In short yes, it stops oil draining back in the off cycle or reduced loading. Inverted P Traps are also used on some cooling towers to stop all the water in the pipe draining each time the pump shuts down.

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: use of inverted P traps

    .

    Yep.

    As stated by Tesla the trap on the top of the riser
    stops the oil from falling back down once it has reached
    the top.

    Regards

    Rob.

    .

  4. #4
    Join Date
    Sep 2012
    Location
    Panama
    Age
    33
    Posts
    12
    Rep Power
    0

    Re: use of inverted P traps

    Good evening to all. I would like to add something I just learned in another forum: inverted P traps should be used at the top of individual suction risers whenever each riser belongs to evaporators which are being connected to a header or main suction line. In this way the oil going through the header does not fall into any of the evaporators during the off cycle. Actually, when I started this post, I was thinking on a single evaporator with a single suction riser. Thank you for your comments.

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: use of inverted P traps

    .

    Suction pipes should always go into the top of the header
    and liquid pipes should always be conected to the bottom
    of the header.

    Regards

    Rob

    .