    cold store formula...



    hello everyone,

    Any calculation for fish storage -25dec cold room load capacity? the room W-36ft, L-32ft, H-19ft

    - compressor
    - evaporator blower

    and it is possible bitzer 4g.2 use for low temp application for -25dec..

    thanks.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: cold store formula...

    Too less in fo to help you any further
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    May 2008
    Location
    malaysia
    Age
    40
    Posts
    82
    Rep Power
    16

    Re: cold store formula...

    ok, any idea and how should i start to do it? and what infomation needed for this?

    can u please advise.

    thanks.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: cold store formula...

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: cold store formula...

    Watt = 25,622.86
    KCal/Hr = 21,962.45
    TR 7.26
    This load is by few assumptions like No Product load & 2 persons in the room & light load as per standard practice.