    Maneurop Compressor shaking on start up



    Has anyone had problems with new single phase maneurop compressors (MTZ28). I have had a few that shake on start up and pull around 44amps before either starting or blowing the circuit breaker or the capacitor. At other times the same compressor has started with no problems. Not sure what to do other than change the brand of compressor which then works fine on the system. Any easy solution???
    Thanks



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Maneurop Compressor shaking on start up

    Flooding in off cycle. crankcase heater duff or if part of a tandem or multiple no nrv on discharge.
    Or maybe none of the above, but it's obviously strugling to get away,could be jumping the springs but would expect it every time.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Jul 2010
    Location
    u.k
    Age
    82
    Posts
    8
    Rep Power
    0

    Re: Maneurop Compressor shaking on start up

    How are the electrics, relay, caps etc,might be worth putting new on.
    Quote Originally Posted by stufus View Post
    Flooding in off cycle. crankcase heater duff or if part of a tandem or multiple no nrv on discharge.
    Or maybe none of the above, but it's obviously strugling to get away,could be jumping the springs but would expect it every time.
    Cheers
    Stu

  4. #4
    Join Date
    Mar 2010
    Location
    usa
    Age
    46
    Posts
    120
    Rep Power
    17

    Re: Maneurop Compressor shaking on start up

    Im assuming the Voltage and start componets are good. Will it start with the Suction and Discharge pressures Equalized?

  5. #5
    Robert88's Avatar
    Robert88 Guest

    Re: Maneurop Compressor shaking on start up

    Does the same when the pressures are equallised. It is running off a 2.5mm lead with a 10amp plug. Do you think this could cause the problem?

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Maneurop Compressor shaking on start up

    What is the length of your 2.5mm lead?
    What is the compressor running amps...as stated on it's specifications label.
    Use a Fluke, or similar meter to do a minimum/ maximum voltage logging to see what the volts drops to during start up.
    Last edited by mikeref; 27-09-2012 at 09:44 AM.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: Maneurop Compressor shaking on start up

    Quote Originally Posted by Robert88 View Post
    Has anyone had problems with new single phase maneurop compressors (MTZ28). I have had a few that shake on start up and pull around 44amps before either starting or blowing the circuit breaker or the capacitor. At other times the same compressor has started with no problems. Not sure what to do other than change the brand of compressor which then works fine on the system. Any easy solution???
    Thanks
    Is this a new installation or a retro-fit?
    Location, United Kingdom

  8. #8
    Robert88's Avatar
    Robert88 Guest

    Re: Maneurop Compressor shaking on start up

    Quote Originally Posted by B G Scott View Post
    Is this a new installation or a retro-fit?
    It is a retro-fit

  9. #9
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Maneurop Compressor shaking on start up

    Quote Originally Posted by Robert88 View Post
    Does the same when the pressures are equallised. It is running off a 2.5mm lead with a 10amp plug. Do you think this could cause the problem?
    Suspect low voltage on start up...Had a chance to do that minimum voltage test yet? (Post #6)
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  10. #10
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: Maneurop Compressor shaking on start up

    Quote Originally Posted by Robert88 View Post
    It is a retro-fit
    First check that the compressor is operating within the design parameters as set out in the selection data provided by the manufacturer.
    As this is already fitted put your amp probe on the supply cable, wind in the suction service valve and start the unit, observe the current drawn and slowly open up the suction service valve and see if you get a smooth start and a current draw in line with the published data.
    If you do consider installing a crank case protection valve in the suction line to limit the suction pressure during pull down to within the limits as detailed in the data sheet.
    When installed check the current drawn on start up and set the valve opening to keep the amps within the tolerance levels indicated by the data sheet.
    Location, United Kingdom