    Ahu cooling coil row calculation



    is there any thumb rule for the no of rows for chilled
    Water
    or dx cooling coil in ahu



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Ahu cooling coil row calculation

    Not that I know of.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2011
    Location
    India
    Age
    38
    Posts
    106
    Rep Power
    13

    Re: Ahu cooling coil row calculation

    Well, if its dealing with full fresh air, a min of 8 row deep is suggested, and for recirculation type with 10-15% fresh air, go with 4 row deep.

  4. #4
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: Ahu cooling coil row calculation

    Surely, if it's full fresh air then you want to maximise the bypass factor so as not to over cool the space ?!

    If so then reduced rows are called for.
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Ahu cooling coil row calculation

    Shouldn't worry Marc, he's a one post wonder from last September

    Although, of course, your observation is valid.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: Ahu cooling coil row calculation

    Brian, I guess it would also depend on occupancy numbers versus load. The higher the occupancy the greater the BPF required. A low occupancy but with a high load would indeed mean more rows required if one wanted smaller ducts and fan i.e. low air volumes.
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.