Results 1 to 8 of 8
  1. #1
    fdharmala's Avatar
    fdharmala Guest

    Unhappy Panasonic Inverter CU-S10JKP error kode H11. Help me..any body



    Some one can help me.? what is meaning error code H11 and how fixed the problem ?



  2. #2
    fdharmala's Avatar
    fdharmala Guest

    Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body

    hello any body ?

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body

    H11 Indoor / Outdoor abnormal communication
    > 1 min after starting
    operation
    Indoor fan operation
    only
    • Internal / external cable connections
    • Indoor / Outdoor PCB

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body

    Troubleshooting
    When abnormality indication starts again
    Is there any wiring error?
    Correct the indoor-outdoor units
    connection wires
    Check the indoor-outdoor units’ connection wires.
    Disconnect terminal 3 wire and measure Vdc between terminal
    2 & 3 from the outdoor unit.
    Is the Vdc fluctuate between 20-70Vdc?
    Replace outdoor PCB
    Reconnect terminal 3 wire and measure Vdc between terminal
    2 & 3 from the outdoor unit.
    Is the Vdc fluctuate between 20-50Vdc?
    Replace indoor unit PCB.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body

    emailed ya the manual- 7meg

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body

    Quote Originally Posted by fdharmala View Post
    hello any body ?
    Steady on there fella.....giving just 4 MINUTES before you start shouting for help is a little impatient

    We don't sit on here just waiting for questions you know

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body

    took me 12 minutes to reply- and e mail manual,must be getting old
    also its been over an hour and no thanks,email reply - cant ask for rep points off a new member
    Last edited by install monkey; 20-09-2012 at 08:17 PM.

  8. #8
    fdharmala's Avatar
    fdharmala Guest

    Wink Re: Panasonic Inverter CU-S10JKP error kode H11. Help me..any body

    Quote Originally Posted by install monkey View Post
    Troubleshooting
    When abnormality indication starts again
    Is there any wiring error?
    Correct the indoor-outdoor units
    connection wires
    Check the indoor-outdoor units’ connection wires.
    Disconnect terminal 3 wire and measure Vdc between terminal
    2 & 3 from the outdoor unit.
    Is the Vdc fluctuate between 20-70Vdc?
    Replace outdoor PCB
    Reconnect terminal 3 wire and measure Vdc between terminal
    2 & 3 from the outdoor unit.
    Is the Vdc fluctuate between 20-50Vdc?
    Replace indoor unit PCB.
    Ok thankyou very much for help me. i'll chek the PCB and if i have any problem i'll give news soon.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •