Short cycling Comp/solonoid
Im having problems with a walk in cold store, the condenser is cycling on
and off via the low pressure switch not because the system is uundercharged I think this is down to the solonoid valve passing or the compressor passing which is the best way to determine this??
-
19-09-2012, 12:29 PM #2
Re: Short cycling Comp/solonoid
Restriction in refrigerant flow, or ambient is low. Is this happening after reaching temperature or during the cooling cycle?
Last edited by mikeref; 19-09-2012 at 12:33 PM. Reason: Read the info Mike..
To the optimist, the glass is half full. To the pessimist, the glass is half empty.
-
19-09-2012, 12:49 PM #3
Re: Short cycling Comp/solonoid
if the solenoid valve freezes (or gets cold) at the end side (in OFF position) then it leaks through, there might be something stuck preventing the pin to close. to check compressor: pump down closing the king valve, observe suction pressure, it it rises, then the compressor is leaking backwards. if replacing the compressor is an expensive thing, then install a time delay ( on make ) to the compressor contactor (set it like 5 minutes), that will increase the compressor lifetime (but will eventually get stuck), I've seen compressors like this run for a couple more years...
-
19-09-2012, 01:11 PM #4
Re: Short cycling Comp/solonoid
Is the solonoid valve de-energised? Even if it is, the comp may still cut in a few times on the LP, just to boil off any gas in the low side. Cheers
In the words of David Byrne, Well...How did I get here?
-
19-09-2012, 05:55 PM #5
Re: Short cycling Comp/solonoid
Shut the reciever valve and see if it still does it (after its had time to pump down)
If it still doing it then its possible its the compressor valves.Mostly found in Oxfordshire, UK :)
-
19-09-2012, 07:04 PM #6
Re: Short cycling Comp/solonoid
All of the above offer sound advise and yours is a knowledgeable assumption.
As the guys agree proving the problem should not be to complicated.
I do have one related question, what's the state of the evaporator like?
If partially restricted or filling incorrectly, even partial oil logging with cause the LP circuit to fluctuate!
( boil off, as 1torr explains!)
Your on the right track already, you just need to be able to spend some time with the problem Gaz.
Follow the guys and your own advise and I am sure you will get there?
Grizzly
-
19-09-2012, 07:13 PM #7
Re: Short cycling Comp/solonoid
All of the above +
Have you checked the cut out / cut in pressures of the LP switch (real life values, not what the markings say)?
.
-
19-09-2012, 07:37 PM #8
Re: Short cycling Comp/solonoid
-
19-09-2012, 07:38 PM #9
Re: Short cycling Comp/solonoid
When it runs? doe's it work ok? pulls temp down as expected? Doe's compressor head gets very hot?
Are there cold spots along the liquid line when it runs? drier not cold?
-
19-09-2012, 09:18 PM #10
Re: Short cycling Comp/solonoid
First of all thanks for all your advice!! Ok to answer some of your questions....
evap coil isn't blocked, when comp is called for fridge temp comes down to 3.0c no probs,
once at temp and comp isn't called for solonoid shuts and it goes off on lp, temp before and
after solonoid seems the same, head of the comp was getting slightly warmer than normal but not too hot to touch, temp seemed to be the same before and after the liquid line drier and I didn't notice any cold spots on the liquid line. also once the unit switches off on lp I get a constant hissing noise.this was only a maintenance visit so I've just reported it so I'll just have to see if I go back to it.
-
20-09-2012, 12:06 AM #11
Re: Short cycling Comp/solonoid
nice, clearly a backwards sound (compressor)