    Cool stuck! please help



    denco high pressure helpneed a bit of guidance.

    Got a denco unit, pressures running at 5.5 bar suction and 15 bar discarge. Which both seem high. Set point is 20 degrees but only getting the room down to 22/23degrees. Tried adjusting the expansion valve slightly but it made no difference... Any ideas anyone?



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: stuck! please help

    What gas is it on??
    what are your air on/off temps on indoor and outdoor??!
    What are the condenser fans doing for head pressure control ? on and off at what pressure/temp.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    david-rock's Avatar
    david-rock Guest

    Re: stuck! please help

    R407c
    Indoor on 23 off 19
    Outdoor on 15 off 28

    Not sure about about the cond fans as there is very little info on unit. There is a fan speed controller running off pressure which is set for 1.9mpa if that helps?

  4. #4
    david-rock's Avatar
    david-rock Guest

    Re: stuck! please help

    R407c Indoor on 23 off 19 Outdoor on 15 off 28

    Not sure about about the cond fans as there is very little info on unit. There is a fan speed controller running off pressure which is set for 1.9mpa if that helps?

  5. #5
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: stuck! please help

    Clean your filters

  6. #6
    david-rock's Avatar
    david-rock Guest

    Re: stuck! please help

    Quote Originally Posted by james10 View Post
    Clean your filters
    First thing I did. Filters and coils spotless.

    Cheers though.

  7. #7
    Join Date
    Mar 2005
    Location
    Birmingham U.K.
    Age
    70
    Posts
    54
    Rep Power
    20

    Re: stuck! please help

    A lot of Denco units have 2 compressors linked into the one refrig system, If this is the case you need to check if both compressor are running.

    If you only have the 1 compressor, carry out a pumpdown to see if the compressor can pull into a vac.

    Bob

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: stuck! please help

    check the controller parameters to ensure its not asking for dehum and powering up the heater banks, check v belts tension, check ur superheat -should be 4degk
    Important
    : "W" and "F" versions are fitted as standard with hot gas by-pass valves
    (hot gas by-pass is an option on "A" versions). On low load room conditions, this
    valve can be adjusted to suit the actual room load. Minimum suction pressure
    suggested is 4.8 bar (70 psig R407C)
    as a last resort check ur gas charge, condenser coils clean, on multi fan coolers ensure all actually work when called for

  9. #9
    Join Date
    Aug 2010
    Location
    England
    Age
    53
    Posts
    77
    Rep Power
    16

    Re: stuck! please help

    Quote Originally Posted by david-rock View Post
    denco high pressure helpneed a bit of guidance.

    Got a denco unit, pressures running at 5.5 bar suction and 15 bar discarge. Which both seem high. Set point is 20 degrees but only getting the room down to 22/23degrees. Tried adjusting the expansion valve slightly but it made no difference... Any ideas anyone?
    Suction pressure is fine and discharge pressure is a little low if anything. Set the head pressure controller to keep the head pressure at 18.2 b,

    Now that you have adjusted the EXV, check your superheat,. It should be between 4 & 9, ish?