    Hi..

    What should be the Factor of Safety to be considered to arrive at the final External Static Pressure of a duct system after adding up the the losses through every straight run and fittings of the critical path?

    Is it enough to take into account the pressure drop for the LAST air outlet in the critical path or should I consider ALL air outlets on the critical path?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Calculating ESP of a duct system

    On the index run you only allow for the resistance of the last outlet......ignoring all other outlets.

  3. #3
    Join Date
    Aug 2012
    Location
    India
    Posts
    9
    Rep Power
    0

    Re: Calculating ESP of a duct system

    Thank you for the response..

    What about the factor of safety?

    Any help is appreciated..

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Calculating ESP of a duct system

    The factor of safety is surely the accuracy of your calculations.

    However, are you asking about the Factor of Safety required when ventilating toxic atmospheres?
    Last edited by Brian_UK; 15-09-2012 at 10:45 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: Calculating ESP of a duct system

    If this is an application in an industrial environment, get a copy of "Industrial Ventilation" published by the
    American Conference of Governmental Industrial Hygienists.
    You will find all the recommendations for most applications with design criteria for most fittings you may come across, including most specialist industrial processes.
    Duct design is dealt with in detail.