Looking for a good instrument to calibrate our pressure transducers for suction and discharge pressure on our Frick ammonia compressors. Anyone have an instrument they recommend for this?
-
25-09-2012, 11:12 PM #2
Re: Pressure transducer calibration
in this maintenance manual calibration procedure for transducers frick, normally reset to zero pressure psig or atmosferic
-
26-09-2012, 02:35 AM #3
Re: Pressure transducer calibration
I would recommend using a High quality Gauge. But be carefull when setting a Offset. Most Transducers I see with a offset are usualy due to a bad connection at the Input, noise in the Cable or a bad Transducer.
-
13-12-2012, 01:53 PM #4
Re: Pressure transducer calibration
Well, most other equipment or gauge will "drift" over time. The only low-cost calibration-grade for pressure transducer is using a device that uses dead-weight.
-
13-12-2012, 03:29 PM #5
Re: Pressure transducer calibration