    Change evaporator



    Hello all.

    In little commercial refrigerating system (hermetic compressor, capillary tube) I used old evaporator (see picture).
    Now in the same little commercial refrigerating system
    I want use new evaporator (see picture)
    Evaporator have not fan.

    New evaporator have area bigger than old evaporator.

    Should I change cap tube length or amount of *****
    or it is optionally?

    Thanks for any advice.
    Attached Images Attached Images



  2. #2
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: Change evaporator

    How much bigger is your new evaporator compare to your old evaporator in size?

  3. #3
    Join Date
    Oct 2005
    Location
    Romania
    Age
    44
    Posts
    66
    Rep Power
    19

    Re: Change evaporator

    i think you will not have any problem..no more *****..and not another capillary tube...
    a bigger evaporator is not a bad thing..especially for static ones
    "do not follow where the path may lead. go instead where there is no path and leave a trail" R.W.Emerson

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Change evaporator

    The capacity of your eveaporator will increase +/- proportionally with the fin area.
    So you have to cut-of a litlle bit the capillary tube and add some refrigerant. It will evaporate higher if you use the same compressor.
    Can the condensor handle this?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: Change evaporator

    No problem at all. Advice, check your volume and flow rate.

  6. #6
    Join Date
    Dec 2005
    Location
    South East England
    Age
    56
    Posts
    155
    Rep Power
    19

    Re: Change evaporator

    By increasing the number of fins you are effectively increasing the surface area of the evaporator & thus it's duty. Also, as a rule of thumb a condenser should be the same size as the evaporator plus 10% to take into account inefficiencies such as heat from the compressor windings being carried over. Ideally you want to know what the duty of the new evap. is & compare it to that of the condenser to see if you still have that 10% difference.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Change evaporator

    If you take your condensor always 10% greater, then it will many times far too litlle.
    You must add at least the absorbed power, take then some margin and select the condensor for this capacity.

    Happy Newyear a good health for all and may this forum grow like it grew the last year.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Designing Roll Bond Evaporator
    By Munzar Ata in forum Fundamentals
    Replies: 11
    Last Post: 05-08-2010, 11:31 AM
  2. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  3. v bone evaporator trouble
    By tranquanghvac in forum Trouble Shooting
    Replies: 0
    Last Post: 26-05-2006, 05:16 AM
  4. Evaporator Design-Air Source Heat Pump for water heating
    By anup in forum Technical Discussions
    Replies: 7
    Last Post: 20-03-2006, 02:26 PM
  5. Searle Evaporator Heaters
    By Abe in forum Commercial
    Replies: 14
    Last Post: 31-12-2005, 10:24 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •