    Cooling in room using ice block

    can we produce cooling in room using ice block.
    place ice bock in the center of room place an impeller in front of it and just control ice drain....
    using this process we can produce cooling?

  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Cooling in room using ice block

    Quote Originally Posted by engr.touseef View Post
    can we produce cooling in room using ice block.
    place ice bock in the center of room place an impeller in front of it and just control ice drain....
    using this process we can produce cooling?
    Yes. but you are limited to the surface area of the ice.

    You could but the ice in a tank of water, pump the chilled water trough a coil and blow air through the coil.

    to control temp just turn the pump off

  3. #3
    Join Date
    Sep 2008
    Location
    India
    Age
    39
    Posts
    24
    Rep Power
    0

    Re: Cooling in room using ice block

    Dear

    You can produce cooling effect by using ICE block but that is very limited for following method.
    1. You put the ICE block in the AHU room at such a place so that return air should contact with ICE block but in this case your humidity in the room increase.
    2. You can use ICE block with water and supply the chilled water to AHU and get the cooling effect.

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Cooling in room using ice block

    Quote Originally Posted by SURESH YADAV View Post
    Dear

    You can produce cooling effect by using ICE block but that is very limited for following method.
    1. You put the ICE block in the AHU room at such a place so that return air should contact with ICE block but in this case your humidity in the room increase.
    2. You can use ICE block with water and supply the chilled water to AHU and get the cooling effect.
    1. is basically incorrect, if the air dew point is above the temp of the ice, then it will lower actually moisture content. "the moisture in the air will condensate out on the ice" RH may increase because you are dripping the dry bulb temp.

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Cooling in room using ice block

    Well,
    In the old days in meat storage rooms they used to build a pile of hay in the middle and place blocks of ice on top.

    So the technique works but with the effort involved and the production losses... Is it really worth it???


  6. #6
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Cooling in room using ice block

    One company in India had used this for emergency purposes for inauguration of a movie hall. The ac system was not working due to some electrical problems. They used Ice in various places & blew air in the hall. It worked very well for the 3 hours time duration. Though some complained later that it was little to cold!!!