    Question RS-485 communication with Carel Mastercella



    Hi;

    For our products we are using Mastercella MD33 type digital controller units. These have RS-485 connection available on them, and you have to install an extra miniature card to enable it. Even we have the card installed, we cannot communicate with the device over RS-485.

    I don't want to invest in a PCo PLC since the local distributor does not want to sell them without software, since they are producing software for the market, and I guess they don't want competition.

    Also according to the manual, you just connect the cables and the RS-485 port on the device handles polarity by itself which causes a major frustration for me. Has anyone been able to communicate with these devices before just using a RS-485 converter or by other means? If you did, how?



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: RS-485 communication with Carel Mastercella

    Hi
    try these:
    http://www.actrol.com.au/install/IR33UserManual.pdf page 17
    http://www.carel.com/carelcom/web/en...id_prodotto=88
    http://www.ecofrigo.no/Portals/0/dok...ool_manual.pdf
    we have connected directly before no problem ,check your registers,and address .
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Feb 2013
    Location
    UK
    Posts
    10
    Rep Power
    0

    Re: RS-485 communication with Carel Mastercella

    Hi
    the reason you are not getting any communication is :
    H0 serial address needs to be changed on each and avoid two units with same serial address, you need to save the parameters so when you change H0 press on Prg and hold it in for 5 seconds to save it.

    polarity is extremely important make sure +,_,GND is in the same order in your network.

    and what type of front end, monitoring system you are using on site.

    Regards,
    Behzad

  4. #4
    Join Date
    Nov 2011
    Location
    Australia
    Posts
    7
    Rep Power
    0

    Re: RS-485 communication with Carel Mastercella

    Standard Carel Mastercella use "Carel protocol" at a baud rate of 19200.

    Typically if you require modbus, the model number is different. The baud rate remains the same.

    What are you connecting to??

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: RS-485 communication with Carel Mastercella

    Behzad, good post
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: RS-485 communication with Carel Mastercella

    pity it was 5 mths later from the original post!!