    panasonic fault codes



    Hi everyone,

    I have been searching for fault codes for a panasonic VRF outdoor unit U-10ME4XPQ and cannot find them anywere. I was sent to change a Compressor and Inverter Board and the unit is showing a fault code U3 on the controller this fault code does not have any of the reference to any of the panasonic codes that I can find. This unit is basically a Daikin with a Panasonic badge on it so both companies are passing the technical help around like a hot potato. I thought I would ask on this site to see if anyone has come across such a problem.

    Cheers



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: panasonic fault codes

    Has the
    check operation
    performed on Outdoor
    unit PC board?
    Press the BS4 on PC board on the
    master outdoor unit for 5 seconds
    or more to execute check
    operation.
    Replace the main PC board on the
    outdoor unit

    thats off a daikin vrv2
    as for panasonic i have no info

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: panasonic fault codes

    Well U3 on a Daikin is a non-completion of the wiring check procedure which sometimes comes up after a power down and power up operation.

    [edit] IM beat me too it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    JawD's Avatar
    JawD Guest

    Re: panasonic fault codes

    As said, that is basically a Daikin unit. The fault codes are identical. Daikin wont touch it though which is fair enough. The issue should be handled by Panasonic or one of their distributors should help.

    As for Panasonic fault codes there are many different lists you need. For VRF there is Panasonic (own brand), Panasonic (Daikin) and now Panasonic (Sanyo).

  5. #5
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19

    Re: panasonic fault codes

    I have a list of Panasonic Fault codes for VRF but all the codes i have start with F. Sorry.

  6. #6
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: panasonic fault codes

    I can't send the fault codes here mail me and I'll send them across Tony.duffy@eu.panasonic.com


    T

  7. #7
    Join Date
    Dec 2008
    Location
    Los Angeles
    Posts
    32
    Rep Power
    0

    Re: panasonic fault codes

    It's been a while, but I think Daikin systems will throw a U3 code (comm signal) like a burp. Try to reset the malfunction history (Clear), and re-commission (re-start) the system. Also check the signal strength from the ODU and furtherest IDU. Have the service manual handy, it is your map to success.

    If that fails, check to see if there have been any changes to the wiring run (lights, transformers, motors, other EMF/EMI loads).

    It is a bad idea to change parts (just the symptom) without knowing the root cause. I do not think the EC was associated with the compressor and inverter board. Both have their own sets of EC's.

    I approach VRF systems as though they are working perfectly. Even if there is an EC. Because more often than not, the EC is correct but the part(s) are good. The EC is could a a 1000 foot view or a 1 feet view depending on many factors. Keep an open mind.

    Please keep us informed as to what the issue ended up being.