    Aug 2010
    windhoek
    41
    coil spec : TD or LMTD
    good day
    what is the norm to spec a coil, TD or LMTD?
    Mar 2008
    232
    Re: coil spec : TD or LMTD
    Depends what you are considering, are you building a coil or just applying a pre-engineered coil
    Location, United Kingdom
    Aug 2010
    windhoek
    41
    specifying performance for pre engineered coil
    Mar 2008
    232
    Ok then you can only consider the TD as the LMTD has already been appraised by the engineer who designed the coil.
    The coil selection is based on the SHR for the design and in imperial units the TD will be selected in the following range.
    SHR 0.95 - 0.80 5 to 8 deg F Below ADP (apparatus dew point)
    SHR 0.80 - 0.50 8 to 15 deg F Below ADP
    All other factors will be tabulated by the engineer who designed the coil and correction factors for capacity against evaporating temperature will be published with the coil specification.