Results 1 to 50 of 103

Hybrid View

  1. #1
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: COP and Superheat - does is it help?

    Come on chef, spill the beans, whats your giving that coolpack does not.

    No system really is even in steady state, there are very few exceptions.

  2. #2
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: COP and Superheat - does is it help?

    Quote Originally Posted by mad fridgie View Post
    Come on chef, spill the beans, whats your giving that coolpack does not.

    No system really is even in steady state, there are very few exceptions.
    Well as I said if you put 50C SH into Coolpack it just plods along and gives very unrealistic answers. It is not possible to continue adding SH and increase the COP ad infinitum so there is something wrong me says.

    What I see is a change in the evap temp so the box temp stays the same and this is real world so the SH is accounted for. My COP drops of quickly at 50C SH