    Hello
    On a cite an ice machine is producing ice flakes whose temperature is 1.5 C . But it should (and is said to prevously do) the ice with - 1C temp.
    I have measured the evaporator SH : 11K (- 27 C evaporation ST, - 16 C gas temp.).
    I have changed TEV's setting and got the SH 5 K (the same - 27 evaporation, -22 C gas leaving temp). During an hour the machine run but the ice temp did not fall.
    What could be wrong with it ? Is not good SH an indication of a proper process ?

    (***** R404A. Glass was full. Also, I have been reducing the temperature of the water entering the evaporator, have also tried different condensation tempertures by changing the fan speed - useless)

    The one of the explanations I have : the ***** is not quite R404A.
    Last edited by Yuri B.; 03-09-2012 at 06:29 PM.



  2. #2
    Join Date
    May 2010
    Location
    United States
    Posts
    47
    Rep Power
    0

    Re: good SH = good process ?

    I'd like to see this 1.5°C ice. Maybe your R718 isn't quite R718?

  3. #3
    Join Date
    Jun 2008
    Location
    Finland
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: good SH = good process ?

    Hi

    SH = Superheat. It means that all liquid refrigerant has evaporated and gas is "over heated" comparing it to evaporating temp.

    So the lower SH = better heat transfer / process, but without liquid separator in suction line SH should be 2-5C and i think that iceflake machines have those.

    I don't have that much experience in iceflake machines to tell is that evap.temp ok or not but i think it's cold enough.

    And that ice temp, maybe you should measure it with another thermometer. Ice temp , even it is mixed with water should have 0C temp
    Last edited by Teuria; 03-09-2012 at 07:05 PM. Reason: Missed point in question

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: good SH = good process ?

    Hi, Yuri B

    Quote Originally Posted by Yuri B. View Post
    Hello
    On a cite an ice machine is producing ice flakes whose temperature is 1.5 C . But it should (and is said to prevously do) the ice with - 1C temp.
    I have measured the evaporator SH : 11K (- 27 C evaporation ST, - 16 C gas temp.).
    I have changed TEV's setting and got the SH 5 K (the same - 27 evaporation, -22 C gas leaving temp). During an hour the machine run but the ice temp did not fall.
    What could be wrong with it ? Is not good SH an indication of a proper process ?

    (***** R404A. Glass was full. Also, I have been reducing the temperature of the water entering the evaporator, have also tried different condensation tempertures by changing the fan speed - useless)

    The one of the explanations I have : the ***** is not quite R404A.

    Maybe I miss something, but how we can have ice with temperature of +1.5*C ? Your thermometer is accurate?

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: good SH = good process ?

    The ice coming out is evidently wet, its temp is slightly positive, it is melting, at the bottom of the vat it is falling in there is water, but they want it to be slightly negative temp, not melting so quickly. The ambient room temp is about 12 C.
    Last edited by Yuri B.; 08-09-2012 at 10:35 AM.

  6. #6
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: good SH = good process ?

    Hi Yuri
    Like some other comments I am not sure how you can have +1.5 oC ice. Pure water freezes at 0oC and if there are any dissolved salts in the water the freezing point will be slightly lower, may need to check your thermometer for accuracy.
    How did you determine the evap temp and the gas temp?
    What type of ice flaker do you have?
    I would have expected the ice to be around -12oC at least if you have an evap temp of -27oC.
    This would only be correct if you are measuring the superheat correctly.
    The ice maker could be oil logged, if this is the case you will have to get rid of the oil out of the evap.
    Give us a a bit more info.
    Regards
    Paul

  7. #7
    Join Date
    Nov 2005
    Location
    canada
    Posts
    11
    Rep Power
    0

    Re: good SH = good process ?

    For r 404 - 27 sounds too low. What are your pressures?
    For Hoshizaki flaker your pressures should be about 30 - 40 lbs suction

  8. #8
    Join Date
    Sep 2008
    Location
    India
    Age
    39
    Posts
    24
    Rep Power
    0

    Re: good SH = good process ?

    Dear...
    Superheat in the system use for safety of compressor to ensure that there should be no liquid refrigerant go to the compressor. If you are using high superheat don't shows that you ice temp increase.

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: good SH = good process ?

    Flaker should be delivering -18'C flake ice, clean and dropping off in sheets, have you checked the salt content . The flaker drum is starved for liquid or possibly saturated with oil. Wet and mushy flake is not good

  10. #10
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: good SH = good process ?

    Thank you for your answers !

    As my "boss" does not allow me to buy instruments I need for the job, I decided to let him solve this problem himself !


    Last edited by Yuri B.; 08-09-2012 at 10:34 AM.

  11. #11
    Join Date
    Jun 2008
    Location
    Finland
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: good SH = good process ?

    Quote Originally Posted by Yuri B. View Post
    Thank you for your answers !

    As my "boss" does not allow me to buy instruments I need for the job, I decided to let him solve this problem himself !
    Hi

    If "The Boss" can fix it or maybe you, let us know what caused that problem.

  12. #12
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: good SH = good process ?

    Hi, Yuri B.

    Quote Originally Posted by Yuri B. View Post
    Thank you for your answers !

    As my "boss" does not allow me to buy instruments I need for the job, I decided to let him solve this problem himself !


    Not sure, but in your original post ... as my "f....r" describe the attitude of your boss much better ... anyhow, let him to solve that problem ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •