    I need a little help with a calculation



    Hello.

    I built a water chiller, and I don't know what its cooling capacity is because I am still learning about these things and it was not built perfectly.

    If it cools 1 gallon of room temperature (25 C) water to 2 degrees celsius, then how many BTUh of heat was removed from the water?


    Visit http://www.kompulsa.com/ for technology news, reviews, and more. Twitter: Kompulsa.

  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: I need a little help with a calculation


  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: I need a little help with a calculation

    We need to know how long it took to cool the water

  4. #4
    Join Date
    Apr 2010
    Location
    Jamaica
    Age
    34
    Posts
    121
    Rep Power
    16

    Re: I need a little help with a calculation

    4 minutes.

    Sorry, the temperature the water was cooled to is actually 10 C. Not 2.
    Last edited by Kompulsa; 03-09-2012 at 01:23 PM.
    Visit http://www.kompulsa.com/ for technology news, reviews, and more. Twitter: Kompulsa.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: I need a little help with a calculation

    You don't say if your Gallon is US or 'Rest of the World'

    As I work in SI lets assume the following:

    1 UK Gallon = 4.8 Lts
    1 US Gallon = 3.8 Lts

    Using the formula Q = M C DT

    Where Q = Power Required in kW
    M = Mass Flow
    C = Specific Heat Capacity
    dt = Temperature difference of working fluid (T1 - T2)

    To use the formula we need to convert your mass into mass flow, so 4.8/240 = 0.02l/s
    Therefore, Q = 0.02 x 4.19 x (25-10)
    = 1.257kW
    Converting kW to BTU's = 4291.9334 BTU's

    If it is US Gallons

    3.8/240 = 0.01583
    Therefore Q = 0.01583 x 4.19 x 15
    = 0.995kW
    Converting kW to BTU's = 3397.3538 BTU's

    I'm assuming that this is a college question?

  6. #6
    Join Date
    Apr 2010
    Location
    Jamaica
    Age
    34
    Posts
    121
    Rep Power
    16

    Re: I need a little help with a calculation

    Sorry, I meant U.S gallons.

    This is for a water chiller that I built with a 50 foot 3/16" copper plain tubing condenser and a 20 foot 1/4" plain tubing evaporator, as well as a 1/4 HP R-134a fridge compressor.

    I tried to cool air with the water but that failed so badly the air was just warm, and air flow was very slow, I could barely feel air coming out of the other side of the heat exchanger and the water the evaporator was in was barely cool. I don't understand if something went wrong when I started trying to cool air, but it cools the water when by itself fine (in the time I showed you).

    This has been tremendously helpful, and it was kind of you to go to that trouble for me.

    Thank you for helping me.

    You answered my question, but now I need to figure out what is happening, and i'm not sure how.

    I'm not sure if my chiller is performing as well as it should as I don't know what the BTU rating at 10 C should be.

    Here is the compressor datasheet, it has a chart of the cooling capacity at different temperatures, but only up to -10, which is 20 C below the temperature I operated it at: http://www.fileconvoy.com/dfl.php?id...ad13bff139f15c

    Does anyone know?
    Quote Originally Posted by frank View Post
    You don't say if your Gallon is US or 'Rest of the World'

    As I work in SI lets assume the following:

    1 UK Gallon = 4.8 Lts
    1 US Gallon = 3.8 Lts

    Using the formula Q = M C DT

    Where Q = Power Required in kW
    M = Mass Flow
    C = Specific Heat Capacity
    dt = Temperature difference of working fluid (T1 - T2)

    To use the formula we need to convert your mass into mass flow, so 4.8/240 = 0.02l/s
    Therefore, Q = 0.02 x 4.19 x (25-10)
    = 1.257kW
    Converting kW to BTU's = 4291.9334 BTU's

    If it is US Gallons

    3.8/240 = 0.01583
    Therefore Q = 0.01583 x 4.19 x 15
    = 0.995kW
    Converting kW to BTU's = 3397.3538 BTU's

    I'm assuming that this is a college question?
    Last edited by Kompulsa; 04-09-2012 at 01:43 PM.
    Visit http://www.kompulsa.com/ for technology news, reviews, and more. Twitter: Kompulsa.

  7. #7
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: I need a little help with a calculation

    To keep us all from changing all your data, try to stick to either imperial or SI. I know it is hard to do while sitting below the big American machine.