    Scotland
    312
    11
    Wink Help fitting Hitachi Horizontal Scroll ZS7516S1
    Hello
    I am fitting a Hitachi horizontal scroll Model ZS7516S1 (see picture).
    It's replacing an obsolete Rivacold compressor for a Pastofrigor Multideck.
    Have I got this right (please see picture):
    The accumulator fits directly onto the suction with no inclination the the left or right - this causes me a problem because I don't think there's enough room under the unit for it.
    Is the high pressure connection on the bottom of the compressor for the capillary tube, presumably for the HP switch and cannot be used for the main discharge?
    All comments welcome.
    Thanks.
    Oct 2007
    manchester
    44
    5,709
    Re: Help fitting Hitachi Horizontal Scroll ZS7516S1
    Scotland
    312
    11
    That'll be the discharge on the bottom then! And the liquid injection will be an option !
    Thanks!
    Scotland
    312
    11
    Can anyone tell me if the accumulator is correctly positioned on this compressor, or does it need to be completely vertical elsewhere in the suction line?
    (I know the liquid injection capillary is sticking out the discharge pipe)