    Chilled water problem

    We use soft water (Hardness < 5 ppm) for our closed loop chilled water system with soft water make-up facility and Chemical Nalco R-39 M. We just change the water 45 days ago but suddenly today we find TDS: 450 PPM, pH: 8.81 & Hardness: 17 PPM. Is it good enough or we need to take any precaution? I try in the Google for any reference for closed loop chilled water system but did not get any authentic papers! So, if any body help me to find any reference.

  2. #2
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Chilled water problem

    http://www.infrastructure.alberta.ca...WTComplete.pdf

    This not heavily technical but also is not commercial....The PH is OK and the TDS is not much higher than one would expect. Was the system flushed before recharging or just locally drained?

  3. #3
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Chilled water problem

    Attached file is excellent usable for me.

    Thanks.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Chilled water problem

    Hi Bashir
    After a complete drain and refill of water system you can expect some inregularities in TDS as you have introduced oxygen to system and probably still air pockets trapped or floating around. Shock dosing can be an option, but monitoring and testing should be daily. You say water supply is softened, but unless you have your own water softener there is no gaurentee local supply is always softened.
    Get chemical suppliers to analyse and recommend action to be taken.

  5. #5
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Chilled water problem

    Thanks.
    We have our own water softening plant and hardness of water hardly exit 1 or 2 ppm. We change the water as per schedule or by checking water quality, but my concern is what are the standard (range of quality parameters) for closed loop child water line?
    Not clear about shock dosing, is it for continuous dosing?
    Last edited by Bashir01219; 31-08-2012 at 03:56 AM.