    Air Source Heat Pump x Water-Water Heat Pump (chiller based) - which is better?



    Hi Guys,
    I need your help and would like you to have your inputs and get the authentic information and clarification on the technical points mentioned below as soon as possible.
    We are the Air Source Heat Pump manufacturer in India. For higher capacity systems like 200 kW plus capacity, we are running in to MNC’s regularly. These manufacturers are suggesting the Water-Water Heat Pump using Return Water at 12oC (max) from Centralised Air Conditioning.
    We can manufacture the system as desired by the customer, but as a technocrat I am not able to convince myself even to quote such system. I may be wrong that’s why need your guidance to improve my knowledge.
    Here the question is not about getting the order but to educate the customer as even today in India, Heat Pump application awareness is not good, rather say, is poor.

    Heat Pump Design Parameters

    Gas R-134a R-407C
    Type Water-Water Air Source
    Condensing Temperature oC 55 60
    Entering Water Temperature oC 50 50
    Leaving Water Temperature oC 55 55
    Heat Source Return Water from AC Atmospheric Air
    Heat Source Temperature oC 9 - 12 20-35

    1. Application
    Primary application is to heat water up to 55-60 deg. C for bathing purpose.
    2. Heat Source
    The average ambient temperature at site location in question is never less than 20 deg. C in the winters when the hot water requirement is most.
    In our opinion, Return Water from Centralised AC which is at 12 deg. C maximum based Water-Water Heat Pump is too low efficient than average 20 deg. C ambient air temperature based Air Source Heat Pump.
    Where as, Water-Water Heat Pump is efficient when you are using Ground Source water as compared to Air Source Heat Pump even in winters as you get the ground water at steady temperature throughout the day, 365 days a year.
    3. Refrigerant
    Customer is insisting upon using R-134a for the system (as suggested by any one of these MNC’s) and we are saying to use R-407C.
    In our opinion, R-134A is best suited for low temperature application like Chiller where as R-407C is having more efficiency than R-134A and is best suited for Heat Pump for water heating application.
    4. Use of By-product
    Water-Water Heat Pump – Chilled water is by-product. But since the heating source water is at 12 deg. C (max), the heating COP drops and entire concept of heat pump for water heating is nullifies.
    Air Source Heat Pump – Cool Air is by-product. – This cool air can be used in TFA or at any place where cooling is required, reducing the cooling load of Centraslied Air Conditioning but maintaining the Heating COP of heat pump.
    5. Cooling Efficiency
    Water-Water Heat Pump – as the condensing temperature is 55 deg. C (in case of R-134A) and water entering temperature is 50 deg. C, the effective Cooling Efficiency (COP) will reduce substantially. In other words,
    Air Source Heat Pump – Air Cooling efficiency is maintained without affecting heating COP
    6. Power Consumption
    Water-Water Heat Pump – As the Entering Water Temperature in Condenser is 50 deg. C, the power consumption will increase. Heating Source is 12 deg. C Air Conditioning Return Water, Heating COP reduces and effective Cooling+Heating COP will reduce
    Air Source Heat Pump – As it is using fresh air (high temperature ambient air) for heating, total COP (Cooling+Heating) will increase.

    In my opinion, either Air Source Heat Pump for tropical conditions like India or Ground Water Source Heat Pump is most efficient Heat Pumps for water heating than the Water-Water Source Heat Pump based on Return Water (12 deg. C) from Centralised Air Conditioner.

    Warm regards

    Anup



  2. #2
    Join Date
    Sep 2005
    Location
    India
    Age
    49
    Posts
    30
    Rep Power
    0

    Re: Air Source Heat Pump x Water-Water Heat Pump (chiller based) - which is better?

    Hi Guys,
    I need your inputs. I have a meeting with the client on Sept 6th, 12.

    Anup

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Air Source Heat Pump x Water-Water Heat Pump (chiller based) - which is better?

    Dear anup

    Sorry about your shortage of time .... here, we all are volunteers - and this is not our primary work (we are struggling for daily bread on some job site), therefore please, be patient ... someone will answer

    Another point, it is not good to post the same post all over ... that makes only confusion to members ....

    Reading your post/s your own answers sound reasonable to me ... but that doesn't mean automatic acceptance to some other people with maybe particular reason to not accept it.

    Please read my sig ...

    I wish you a good luck with answers you need.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Sep 2005
    Location
    India
    Age
    49
    Posts
    30
    Rep Power
    0

    Re: Air Source Heat Pump x Water-Water Heat Pump (chiller based) - which is better?

    Hi Josip,
    Thanks for your reply and sorry for uploading at 2 forums.
    There were many views to my post but no reply. I was worried whether my presumptions were wrong. You guys are really masters in technology and I have very high regards to all of you for your knowledge. Validation from RE experts is more important for me.
    I am deleting this thread from this forum.

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Air Source Heat Pump x Water-Water Heat Pump (chiller based) - which is better?

    If you are always utilizing 100% of the cooling and heating side (presume heating will always be similar), then it simply comes down to SST (Te) higher the SST the more efficient.
    So keeping it simple water entering 12C, then SST will be around 8C, air on will 20C+, SST will be about 14C.
    The unknown is the cost of moving the water or the air, which needs to be calculated into the overall COP.

  6. #6
    Join Date
    Sep 2005
    Location
    India
    Age
    49
    Posts
    30
    Rep Power
    0

    Re: Air Source Heat Pump x Water-Water Heat Pump (chiller based) - which is better?

    Thanks Mad Fridge. Cost of moving the water and the air is almost similar.