26-08-2012, 11:02 AM #1
Carrier 30GH EXV problem
Hi all!
I have an unusual problem. I changed EXV to TXV + liquid line valve, but can't find output from controller to liquid valve. Without pump down the chiller don't work properly. Can anybody help me with this issue?
-
26-08-2012, 11:38 AM #2
Re: Carrier 30GH EXV problem
cant find any info on a 30gh
-
26-08-2012, 11:53 AM #3
Re: Carrier 30GH EXV problem
-
26-08-2012, 12:48 PM #4
-
26-08-2012, 01:12 PM #5
Re: Carrier 30GH EXV problem
thanks for your answers guys.
If I cant reconfigure controller's parameter, maybe you know how to disable pump down function
-
26-08-2012, 01:17 PM #6
Re: Carrier 30GH EXV problem
hi
can you give me please more information how to make these changes
thanks
-
26-08-2012, 01:18 PM #7
-
26-08-2012, 02:58 PM #8
Re: Carrier 30GH EXV problem
hi again guys
anybody know how can i activate liquid line valve outputs from the controller?
this is realy can solve this problem
-
26-08-2012, 04:12 PM #9
Re: Carrier 30GH EXV problem
Hi
the exv is the pump down valve !!
since you are running a pro dialog plus i would change to a standard exv and control it seperatly ,we have done this before with great succces,
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
26-08-2012, 09:05 PM #10
-
27-08-2012, 05:37 AM #11
Re: Carrier 30GH EXV problem
Dear dennis,
You can’t fix the TXV on chiller 30 GH series. The prodialog processor equipped with only EXV.
But you can run the chiller by using 3 ways,
- Either fixed back the original new EXV.( you did not mention the reason of the replacement of exv to txv)
- Or prepare and design schematic electrical control drawings with relay logic considering the unit capacity by using stage controller (ex: Siemens rw68) for this job need skill and good field experience.
- Or you can convert the 30 GH to 30 GT by replacing the processor board and required the control alteration. (We have done this successfully in field).
Last edited by moideen; 27-08-2012 at 05:40 AM.
-
27-08-2012, 09:44 PM #12
Re: Carrier 30GH EXV problem
hi guys
thanks for your response. i did an awfull combination and my 30gh started work without EXV.
-
28-08-2012, 05:13 AM #13
-
28-08-2012, 12:39 PM #14
Re: Carrier 30GH EXV problem
Yes sure.
I took relay 12 VDC and connect it to the output from 30GH EXV controller. for filter noises from the EXV normal operation i put timer off-delay with 30 sec. delay. so when controller make pump down it send continiusly close to EXV at this moment timer change it position and send off to the liquid valve.
i know that it is not very good solution but it work.
-
28-08-2012, 02:01 PM #15
-
28-08-2012, 07:34 PM #16
Re: Carrier 30GH EXV problem
What is the model number of your 30GH and what type of controller does it have Flotronic 2 or Pro Dialog. Unless you have changed the configuration of the controller your chiller will still think it has a EXV and as such you are likely to encounter pronlems.
Last edited by Gibbo; 28-08-2012 at 07:36 PM.
-
29-08-2012, 06:13 AM #17
Re: Carrier 30GH EXV problem
hi
i adjusted superhit 6.5 - 7 degrees. with this parameters chiller have a very stable work.
low pressure 68 psi. high pressure 300 psi water in 13 degree celsius
in the attachment you can see my diagram
-
29-08-2012, 06:17 AM #18
Re: Carrier 30GH EXV problem
hi Gibbo
chiller model 30gh-068 with pro dialog controller.
do you have information how to change factory settings i'll be very gratefull if you share it with me
thanks
-
29-08-2012, 08:21 PM #19
Re: Carrier 30GH EXV problem
If the Pro Dialog Controller is black you will not be able to change factory configuration, can only be done by Carrier. The factory config needs to be changed from EXV to TXV as well as the Head Pressure control setting from EXV control to setpoint control.
-
30-08-2012, 06:34 AM #20
Re: Carrier 30GH EXV problem
Exv is pulsed DC. It has 5 wires and dc voltage is not constant on any each wire. Always voltage is varying as per the compressor superheat. Then how did you activate the dc relay? Can you clarify the relay logic and operation sequence? You have used two “NO’ for completing the circuit from timer!!Moideen-Dubai
-
30-08-2012, 08:35 AM #21
Re: Carrier 30GH EXV problem
how i have been said before it's not work properly ( but staible). relay have a lot on/off circles. at the stop of the compressor work EXV bord send continiusly 12 volt signal. timer tought it and deactivate the liquid valve. for minimizate on/off circles we put diodes. i took 4 wires with diods to the negative pole of the relay coil and red wire to the positive.
"You have used two “NO’ for completing the circuit from timer"
what does it mean ?
can you give me more information how to convert 30gh to 30gt. when you replace a chip you need to program controller. do you have factory setting? which program you use connect for connect to the controller?
thanks
-
30-08-2012, 10:42 AM #22
Re: Carrier 30GH EXV problem
What was the original problem, you seem to be reinventing the wheel here with all of these modifications.