    Charging formula



    sorry to talk shop over the festive period, but i am looking for a formula for accurately charging up an ac system, if anyone knows of any links where i could find this it would be much appreciated. merry christmas.

    Zimbo



  2. #2
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Charging formula

    Charging is strictly by weight

    You also refer to your gauge pressure to ensure the evaporating temp is right
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  3. #3
    Join Date
    Dec 2005
    Location
    Spain
    Posts
    61
    Rep Power
    19

    Re: Charging formula

    Have never believed refrigerant charging to be an exact science.... In over 20 years have never met a system to be at its optimum with the calculated charge.... or even two identical systems to behave the same.... but thats a different story! Refrigerant charging should be done while taking many different things into account, some of which are pressures, state of coils and pipes, liquid line flashing.... the list is probably far longer than i could produce with my limited knowledge. A reasonable engineer will take all these things into account while achieving the best balance.
    Last edited by Lazarus; 26-12-2005 at 02:44 PM. Reason: my spelling as usual
    :cool: Calvo :cool:

  4. #4
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Charging formula

    On your outdoor unit there is a "nameplate" which will give you info on the Model, Serial number, etc

    It will tell you also what refrigerant and the quantity.


    System is usually precharged for a 7 metre pipe run. Check with the manufacturer .

    You add so many grammes per extra length of pipe run, or remove refrigerant accordingly.

    Refer to the manual which comes with the system.
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  5. #5
    Join Date
    Nov 2005
    Location
    USA, New Jersey
    Age
    60
    Posts
    16
    Rep Power
    0

    Re: Charging formula

    If your dealing with a specific manufacturers unit and the charging info is not with it, contact the company for either the specific weight of charge or the psychometric charging table for the unit. If neither of these is available I have used a mthod for years that works well for me. Obviously we are refering to a fixed metering device and not a TEV. Charge the system, SLOWLY, to obtain a 10 degree F subcooling and a 10 to 15 degree F superheat with the unit at temp. It is important that the box be at its design temp. because the subcooling and superheat change dramatically from the point of start up till you meet design conditions. As long as all other variables are normal and the coils / compressor etc. is still factory spec. you should be ok with this method.

    Chill

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Charging formula

    There isn't such a thing as a simple phormula for charging an airco
    If it should be that simple, then there should be not such a shortage of techs, just learn some phormulas out of your head and your a qualified tech.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Charging Split, Using Amps
    By Robearbam in forum Fundamentals
    Replies: 16
    Last Post: 08-06-2011, 09:05 PM
  2. 410a charging
    By gwilliamson in forum Air Conditioning
    Replies: 39
    Last Post: 17-11-2010, 05:03 AM
  3. Refrigerant charging weighing scale
    By malik55 in forum Tools and Calculators
    Replies: 4
    Last Post: 06-11-2006, 11:14 PM
  4. Car a/c charging chart
    By chilly in forum Transport
    Replies: 7
    Last Post: 07-09-2005, 08:18 AM
  5. Charging Adaptor for BMW
    By Abe in forum Air Conditioning
    Replies: 6
    Last Post: 11-09-2002, 08:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •