    Ice rink- recovered heat question



    Recovered heat from ice rink refrigeration condenser can be used in a variety of applications: space heating, domestic water heating, floor heating, ice melting, ventilation....
    Is there by any chance possibility to assume what would be a minimum of recovered energy in every moment, in order to minimize a district heating connection design capacity?(e.g. lets say thath in total I need 400kw, and that I could say that from refregaration plant I'll get 150kW. in that cases I would need 250 kW more taken from district heating)?.

    Best regards,

    Drmile



  2. #2
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Ice rink- recovered heat question

    What are you going to heat air or water? What is the target temperature?

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Ice rink- recovered heat question

    Where do you get your heat from when the system is off cycle on thermostat?

    if your 400kW requirement is constant, you will have a shortfall

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Ice rink- recovered heat question

    Your heat rejected heat is: KW absorbed by the compressor + KW cooling capacity.

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Ice rink- recovered heat question

    The nominal heat recovery you can get depends on the magnitude of the refrigerant plant.

    You can use a water tank to store heat water so you can assure a certain amount of heat when the refrigerant plant is OFF or temporally stopped by the ice temperature.

    Quote Originally Posted by drmile View Post
    Recovered heat from ice rink refrigeration condenser can be used in a variety of applications: space heating, domestic water heating, floor heating, ice melting, ventilation....
    Is there by any chance possibility to assume what would be a minimum of recovered energy in every moment, in order to minimize a district heating connection design capacity?(e.g. lets say thath in total I need 400kw, and that I could say that from refregaration plant I'll get 150kW. in that cases I would need 250 kW more taken from district heating)?.

    Best regards,

    Drmile
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Nov 2003
    Location
    holland europe
    Age
    65
    Posts
    78
    Rep Power
    21

    Re: Ice rink- recovered heat question

    as a fist all the power to the compressor can be used as heat.
    however in winter time the demand is a lot lower, and the temp needed for the heat is so high the ice rink will not be efficient. so design should be full heat from city in worst case scenario.