    Recovered heat from ice rink refrigeration condenser can be used in a variety of applications: space heating, domestic water heating, floor heating, ice melting, ventilation....
    Is there by any chance possibility to assume what would be a minimum of recovered energy in every moment, in order to minimize a district heating connection design capacity?(e.g. lets say thath in total I need 400kw, and that I could say that from refregaration plant I'll get 150kW. in that cases I would need 250 kW more taken from district heating)?.
    Best regards,
    Drmile
    Sep 2008
    Canada
    772
    12
    Re: Ice rink- recovered heat question
    What are you going to heat air or water? What is the target temperature?
    Oct 2001
    Nottingham UK
    5,123
    42
    Where do you get your heat from when the system is off cycle on thermostat?
    if your 400kW requirement is constant, you will have a shortfall
    I'm back on the Pale
    Sep 2003
    ISRAEL
    66
    4,151
    38
    Your heat rejected heat is: KW absorbed by the compressor + KW cooling capacity.
    Dec 2008
    Portugal
    42
    1,040
    13
    The nominal heat recovery you can get depends on the magnitude of the refrigerant plant.
    You can use a water tank to store heat water so you can assure a certain amount of heat when the refrigerant plant is OFF or temporally stopped by the ice temperature.
    Quote Originally Posted by drmile View Post
    Best regards,
    Drmile
    Nov 2003
    holland europe
    15
    as a fist all the power to the compressor can be used as heat.
    however in winter time the demand is a lot lower, and the temp needed for the heat is so high the ice rink will not be efficient. so design should be full heat from city in worst case scenario.
    computer shooter
    paul deelen
    +31653300739