    vrv 111 fault



    Hi can anyone help me with ao fault on daikin, someone has been tampering with the settings in the remote and i would like to get the unit back to its default settings to see if the AO fault disappears, would any one know the sequence of buttons to push so i can try this. any help will be much appreciated.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: vrv 111 fault

    ao- is external protection device- outdoor fault
    to reset a fault, push bottom left button so the fault cade is displayed,hold the on/off button for upto 10seconds,when a0 changes to 00 then try to restart the unit, sometimes outdoor unit req powering down then restarting

  3. #3
    robbie's Avatar
    robbie Guest

    Re: vrv 111 fault

    thanks for the info, i will give it a go and see if i have any joy

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: vrv 111 fault

    Quote Originally Posted by install monkey View Post
    ao- is external protection device- outdoor fault
    to reset a fault, push bottom left button so the fault cade is displayed,hold the on/off button for upto 10seconds,when a0 changes to 00 then try to restart the unit, sometimes outdoor unit req powering down then restarting
    Good answer regarding how to clear the last fault code.....but if he doesn't rectify the fault it will keep re-appearing