    This alarm appears on the display, the machine is stopped:

    STRATER MALFUNTION DETECTED

    and Replace, relay board, digital board, power supply and rectifier diode.

    I have another point to check?


    you will have to manually change the real time clock?

    thanks



  2. #2
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: YORK YSCACAS2 style C

    Hi
    it would seem the vsd you have has a power supply problem .
    check all the flat cables and connections
    when replacing the main card the clock will need to be reset .
    this seems like a very vague fault message!!
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  3. #3
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    77
    Rep Power
    13

    Re: YORK YSCACAS2 style C

    Check the electronic protection of the compressor motor, it is connected in series to the coil of the power contactors and causes alarm of missed departure.

  4. #4
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: YORK YSCACAS2 style C

    no vsd
    electromecanique starter

  5. #5
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: YORK YSCACAS2 style C

    Hi
    check your contacs that feed back an input to the controller on contactors status.
    i would also heck your relay board.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  6. #6
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: YORK YSCACAS2 style C

    goshen:

    I changed the following parts:

    relay board
    power supply
    diode rectifier
    digital input
    CM2
    the RTC would have some relation with this problem?