    Thumbs up Carrier 30 XA 1252 OIL problem TU3WHH6003 Carlyle .



    Hi guys sorry to bother but I am not very good with those compressor ...

    So leak on Muffler oil everywhere PROBLEM ! I change muffler , filter drier core doing leak test now 15 bar 1 - How much oil could be gone ???
    2 - Should I change all oil ???
    3 - If yes how much oil ?


    oil test is positive just wonder what exactly should do next fix it properly ...
    Attached Images Attached Images



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Carrier 30 XA 1252 OIL problem TU3WHH6003 Carlyle .

    Hi palkoper.
    Do you mean by saying the oil is positive that it is good or bad?

    I am assuming that you mean its good, therefore you need to check the level at the oil separator.
    Which should have a level in the top glass.
    If you need to add oil, the recommended method is to pull a vacuum on the oil separator.
    And draw the oil into the system through the oil header this will also ensure the oil header if full.
    On start up check your oil differential and pressure.
    Grizzly