17-08-2012, 01:04 PM #1
r410 low ref effect
hi every one
i work in thermal power plant
since many years we used r22 ac unit in it
they were sucssful
before amonth
we been supplied by ac unit but with r410
problem is the cooling of these unit was too weak
so we tried many mark of ac
lg.samsung etc
same result
since the temp in iraq reaches 51 c in some days
so where is the problem
in ***** 410
or in the unit or where
can some one advice me
-
17-08-2012, 06:20 PM #2
Re: r410 low ref effect
r410a is twice the operating pressure of r22
discharge pressure is typically 33 bar- at 20deg ambient so at 50 deg ambient, high head pressure and poor performance
-
18-08-2012, 12:54 AM #3
Re: r410 low ref effect
thank u for ur reply
as u know the normal suction pressure is 60 psi
but when temp exceed 50 c and reaches about 60 and 70c
pressure is rise to 80 psi
so what u advice me to do
-
18-08-2012, 07:30 AM #4
Re: r410 low ref effect
To the optimist, the glass is half full. To the pessimist, the glass is half empty.
-
18-08-2012, 02:20 PM #5
Re: r410 low ref effect
-
18-08-2012, 05:50 PM #6
Re: r410 low ref effect
They are too weak for the present load. Check their specifications for the efficency at such ambient temperature. In all, if the choice of the units was based on a claimed efficiency ratio, then the mistake is now tangible.
-
18-08-2012, 05:53 PM #7
Re: r410 low ref effect
They are too weak for the present load. Check their specifications for the efficency at such ambient temperature. In all, if the choice of the units was based on a claimed efficiency ratio, then the mistake is now tangible.
So, at first check the "papers," as Mikeref said.
-
17-01-2013, 11:04 PM #8
Re: r410 low ref effect
thank u for help
please close the thread