    Question Help Me



    Here i have a chiller with reverse return piping to cool down the machines.i want to add up a new machine in the chilled water circuit. How should i incorporate it in the circuit.it has 2" piping connections and 400ft apart from the chiller and other machines.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Help Me

    I would suggest a separate, pumped, circuit connected to your main lines.

    Are you going to uprate your main chilled water pumps to allow for this extra flow?
    Brian - Newton Abbot, Devon, UK