    Clivet Chiller fault



    Hi all,

    just took over new site with 2 identical Clivet water chillers approx 5 years old. I havent got the model number to hand.
    Upon arrival i found 1 chiller in fault and not running. fault is E 107 fan/pump thermal cut out alarm.This fault would not reset. Found overload for all 5 condenser fans tripped (22amps) reset and it tripped. reset again and stayed on but the alarm wont reset on controller. I wont be back there til next week and was just wondering on any ideas??
    Condenser fan motors are 3 phase and one cable goes to junction box from control panel and then feeds all fans.
    Is there thermal protection on these fans and one is dodgy?

    Many thanks not much experience on clivet chillers,
    Gary



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Clivet Chiller fault

    CLIVET UK LTD
    4 Kingdom Close, Segensworth East - Fareham, Hampshire - PO15 5TJ - United Kingdom
    Tel. + 44 (0) 1489 572238 - Fax + 44 (0) 1489 573033 - info@clivet-uk.co.uk

  3. #3
    Join Date
    Dec 2011
    Location
    Ireland
    Age
    43
    Posts
    51
    Rep Power
    13

    Re: Clivet Chiller fault

    thanks IM i can ring them, was just interested if anyone has similar experiences on these chillers

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Clivet Chiller fault

    Hi Gary.
    Basically if the fault is not isolated your chiller could still be locked out.
    You should have a reference to which circuit is causing the issue as well?
    If not then start metering your condenser fans. Or disconnecting them, to identify which is causing the issue.
    Grizzly


    E107 Fan thermal cut-out alarm Manual Stop circuit in question (see example) If the
    ventilation is in common, shut-down “UNITi

    Example:
    U2-CMP2
    (Alarm Unit-2 / Compressor Module 2)
    E105 High pressure alarm
    Indicates that the alarm condition is active on Compressor Module 2, Unit 2

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Clivet Chiller fault

    All fans' inner thermal contacts may be connected in series, at least one is opened.