Results 1 to 18 of 18
  1. #1
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Moisture in POE or PVE oil



    If POE or PVE oil has taken up moisture(compressor stood to long open for example), can it be taken out again by vacuuming it (low enough and long enough)? Anyone experienced already with this?


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Moisture in POE or PVE oil

    I think the moisture chemically changes the POE oil, not sure with PVE.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Moisture in POE or PVE oil

    Hi Peter.
    Some may have tried?
    However whenever I have encountered a moisture laden synthetic oil.
    I have drained and replaced the oil, did this system not have a crankcase heater?
    The absorption properties of some oils are much greater than a vacuum can remove.
    Some will absorb 10% of their volume overnight if left exposed to the surrounding atmosphere.

    IE the cap is left off the can.

    Grizzly

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Moisture in POE or PVE oil

    Grizzly, these are scrolls in VRV machines and their's no drain on it. So removing the oil without taking out the compressor is very difficult. There's a crankcase heater which can help to vaporize the diluted moisture in the oil. After analyzing a sample of oil, we foud nmoisture in it but question remains if this could be taken out by vacuum it properly. Is the moisture somehow a prove that teh vacuum process wasn't done very well.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Moisture in POE or PVE oil

    Earlier discussions on this suggested that the moisture combines with the oil to form a new compound which vacuuming may not remove, i'm not so sure though surely a deep enough vacuum, triple evacuation would remove a large percentage of the moisture allowing the drier to trap the rest?

    al
    Mostly found in the southern part of this green and pleasant land.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Moisture in POE or PVE oil

    Interesting little article...
    http://www.rses.org/assets/journal/0110_MSAC.pdf

    This also seems to be common comment - "POE oil bonds with water on a molecular level, and a filter drier is the only way to remove it."

    Also a report, below, makes this statement - "It has previously been reported many times that Polyolester will hydrolyze under certain conditions and Polyvinylether will not hydrolyze because of its ether structure. This can be reconfirmed through this study."

    http://docs.lib.purdue.edu/cgi/viewc...5&context=icec
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Moisture in POE or PVE oil

    Nope. Surface tension of various grades of oil is prohibitive Peter.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  8. #8
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Moisture in POE or PVE oil

    Peter,
    You had to open that big can that clearly stated "WORMS" on it, didn't you...

    So here goes:

    I once had a chat with a chemist involved in the manufacturing of POE oils and asked the very same question.
    (Well, my question was more in line with "what does it mean that the new oils are hygroscopic and what impact does it have" but anyway)

    The answer started something like this:
    "said refrigerator oil contains as base oil components a polyol-ester oil formed by reacting a fatty acid with a polyhydric alcohol selected from Pentaerythritol (PET), trimethylolpropane (TMP) or neopentylglycol (NPG), to which are added 0.1% to 2.0% by weight of tricresylphosphate (TCP) and 0.01% to 10% by weight of an epoxy compound, wherein the epoxy compound comprises glycidyl ether or 0.01% to 10% by weight of carbodiimide"

    To you and me it roughly translates to:
    POE oil is made by mixing an acid with a lot of other chemicals and getting a very acidic and corrosive mixture that will eat through most metals (incl. copper and steel) if left in that state. Only by removing H2O (water) molecules from this mixture will it
    neutralise and become non acidic.
    When they make the oil, the moisture is removed by vacuum.
    Unfortunately the end result is a hygroscopic oil (it absorbs moisture) and as soon as it get any moisture in it it will become acidic.
    The good news is that the process can be endlessly repeated, by exposing the oil to a deep vacuum the moisture will be removed and the oil will again become neutralised.

    How deep the vacuum needs to be depends on the temperature, generally it is accepted that 500micron (1/2 Torr) will do the trick. The important thing is that the vacuum is standing, without any increase in pressure. This is why a good digital vacuum gauge with micron scale is needed. When you reached the desired vacuum level, isolate the system and turn the vacc pump off, any increase in pressure from then on indicates that there still is moisture in the oil.

    Deeep breath...

    Class, any questions?
    Are you still awake?



    .
    Last edited by The Viking; 14-08-2012 at 11:32 PM.

  9. #9
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Moisture in POE or PVE oil

    Viking. If the PPM of moisture in the oil is low enough and several days are allowed on vac, then i might accept your reply. If there is enough moisture to form a small "Puddle" of water under the oil... i would still stand by my previous post Nice breakdown in your description though.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Moisture in POE or PVE oil

    So you'd need 500 microns at the bottom of the sump etc, the weight of oil above would have an effect on the level of vacuum throughout the oil i think?
    Mostly found in Oxfordshire, UK :)

  11. #11
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Moisture in POE or PVE oil

    Quote Originally Posted by monkey spanners View Post
    So you'd need 500 microns at the bottom of the sump etc, the weight of oil above would have an effect on the level of vacuum throughout the oil i think?
    G'day M.S. Going by your last video in "what we did today" i think there was actually OIL contamination in the compressor, rather than moisture
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Moisture in POE or PVE oil

    Quote Originally Posted by mikeref View Post
    G'day M.S. Going by your last video in "what we did today" i think there was actually OIL contamination in the compressor, rather than moisture
    Think that one was using water as the lubricant! Would have been interesting to try and get it running again but they scrapped it.
    Mostly found in Oxfordshire, UK :)

  13. #13
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Moisture in POE or PVE oil

    @ Mike,
    In your scenario with the water the vacc gauge would rise rapidly, if you got a (deep)standing vacuum there is no more moisture left. You would be surprised how fast this can happen, it all depends on volumes and just how much water there were to start with. But you do need a decent digital vacc gauge to tell you that there isn't any rise of the pressure.

    @ Monkey Spanners,
    You are of course right, the weight of any fluid will have an impact on pressures.
    As nature would try to keep the concentration of water molecules equal within the oil it should be enough if the surface of the mixture were at a deep vacuum, it would just take longer to boil all moisture off.
    Also, 10 meter of water column = 1 Bar. Oil is slightly lighter but anyway, how deep is the oil level in a normal sump? 0.05m / 0.005Bar?


    On the other hand, has anybody ever heard of a compressor failing because it had the oil changed once too often???
    (Just remember that the new oil when transferred from the can to the compressor most likely will absorb moisture and therefore require a vacuum before the compressor is recommissioned, not like the good old days when you just left a bit of pressure in the crank and pumped the oil in before you restarted the system)
    Last edited by The Viking; 15-08-2012 at 12:54 AM.

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Moisture in POE or PVE oil

    Thanks so far all of you. You can't believe how important all these answers and practical experience are right now ;-) The future in refrigeration business of a good colleague depends now on such a knowledge. See also my other questions in the same section. All related to the same problem.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Moisture in POE or PVE oil

    Viking

    Great reply, i've to slut some love around before being able to rep you!!

    any chance you would have that in an ahem "official" publication?

    Mike, wouldn't "boiling" the oil break the surface tension allowing the moisture escape?

    al
    Mostly found in the southern part of this green and pleasant land.

  16. #16
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Moisture in POE or PVE oil

    G,day Al. Have to say that i've not been down that road. If compressor oil is known to be contaminated with moisture, i'll find a way to change it rather than spend a lot of time on vac.
    There was a job many years ago where i spent 8 days trying to remove moisture.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  17. #17
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Moisture in POE or PVE oil

    Very true Mike, but the design of these units defeats oil changes without literally tipping the compressor on its side!
    Mostly found in the southern part of this green and pleasant land.

  18. #18
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Moisture in POE or PVE oil

    Hi!

    When you have moisture in circuits containing POE oils, the contamination grows gradually with the exposition of the oil to the humidity. The problem to remove the oil, is that it gets trapped in the circuit syphons and you cannot remove it just with a deep vaccum. Moreover, in case you have water, the oil film will remain above it, avoiding this way the water evaporation.

    Thing is, if you have not removed the whole content of contaminated oil, and moisture, the next charge of oil will get contaminated as well, and create a corrosive ambient in the circuit at mid term.

    So, firstly, you need to totally eliminate the oils, and then remove the moisture with vaccuum and nitrogen as usual.

    Regards,

    Nando.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •