30-08-2012, 11:16 AM #1
Chilled water problem
We use soft water (Hardness < 5 ppm) for our closed loop chilled water system with soft water make-up facility and Chemical Nalco R-39 M. We just change the water 45 days ago but suddenly today we find TDS: 450 PPM, pH: 8.81 & Hardness: 17 PPM. Is it good enough or we need to take any precaution? I try in the Google for any reference for closed loop chilled water system but did not get any authentic papers! So, if any body help me to find any reference.
-
30-08-2012, 10:07 PM #2
Re: Chilled water problem
http://www.infrastructure.alberta.ca...WTComplete.pdf
This not heavily technical but also is not commercial....The PH is OK and the TDS is not much higher than one would expect. Was the system flushed before recharging or just locally drained?
-
31-08-2012, 12:26 AM #3
Re: Chilled water problem
Hi Bashir
After a complete drain and refill of water system you can expect some inregularities in TDS as you have introduced oxygen to system and probably still air pockets trapped or floating around. Shock dosing can be an option, but monitoring and testing should be daily. You say water supply is softened, but unless you have your own water softener there is no gaurentee local supply is always softened.
Get chemical suppliers to analyse and recommend action to be taken.
-
31-08-2012, 03:49 AM #4
Re: Chilled water problem
Thanks.
We have our own water softening plant and hardness of water hardly exit 1 or 2 ppm. We change the water as per schedule or by checking water quality, but my concern is what are the standard (range of quality parameters) for closed loop child water line?
Not clear about shock dosing, is it for continuous dosing?Last edited by Bashir01219; 31-08-2012 at 03:56 AM.
-
31-08-2012, 03:52 AM #5
Re: Chilled water problem
Attached file is excellent usable for me.
Thanks.