    Heat Release from a human body
    How much heat release per hour (in watt) form a adult human body ? Which need to consider to calculate cooling load of a room?
  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,127
    Rep Power
    42
    Re: Heat Release from a human body
    CIBSE guide gives between 90W and 140W depending on how energetic the people are. Someone sitting at a desk Tweeting or on Facebook will be nearer 90W and someone doing manual labour will be nearer 140W
    I'm back on the Pale
  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    66
    Posts
    4,152
    Rep Power
    38
    When the ambient is higher then your temp. the body absorbs heat,[will never accrue in the UK]
  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,477
    Rep Power
    39
    As Frank says, it varies.
    The figures he quotes are generally OK but just be aware that not everybody falls within the norm.
    My wife for example - 0W...
    Young ladies in a gym - anything up to 1kW depending on how many men are watching.
  5. #5
    Join Date
    Nov 2009
    Location
    Bangladesh
    Age
    31
    Posts
    6
    Rep Power
    0
    Very Nice replay