21-11-2005, 08:31 PM #1
Control circuits
Hi
Does anyone know of a link for starting methods for 3 phase semi hermetic compressors.
Thankyou.
Bernard
-
21-11-2005, 08:54 PM #2
Re: Control circuits
Hi Bernard!
Starting method (Not important what type compressor)depends very much from power of the motor
It is very nice idea do it with the softstarter.
-
21-11-2005, 09:00 PM #3
Re: Control circuits
Hi bernard,
Is this what you mean?
http://www.johnson-pump.com/Horticul...tart-motor.htm
OR
http://www.cacciaelettronica.it/products2_2117.htm
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
21-11-2005, 09:19 PM #4
Re: Control circuits
Hi bernard,
A soft start is a good one.
YY is another one.
And direct start.
These are the most common ways to start a semi hermetic compressor.
Chemi
-
21-11-2005, 11:44 PM #5
Re: Control circuits
Originally Posted by bernard
http://www.lmphotonics.com/m_start.htm
-
24-11-2005, 08:15 PM #6
Re: Control circuits
Thankyou
The links gave me all the info I needed,sorry for the delay in my response but I,m just so busy with work at the mo.
Kind Regards
Bernard
-
25-11-2005, 08:16 PM #7
Re: Control circuits
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
26-11-2005, 09:05 AM #8
Re: Control circuits
Thanks Peter
Most of the part wound motors I have seen have their timers set for 1 second.Is this a standard setting or should it vary depending on size ?????
Thankyou
Bernard
-
26-11-2005, 10:12 AM #9
Re: Control circuits
We set it also that short: 1 sec.
In Y-D start you have to set the time as long the current in Y isn't 'flattened' . You can only set this by measuring the start AMP's and time when the current drops and stabilises. This will be the time for the Y-run.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
Airwell Florida Inverter Air Condition - in need of help
By AndY1 in forum Air ConditioningReplies: 21Last Post: 05-07-2008, 10:48 AM -
Control scenario
By Mike Hopkins in forum Technical DiscussionsReplies: 5Last Post: 14-09-2007, 11:25 AM -
Short Cycling blues & low pressure control switch
By mccoolair@yahoo in forum Supermarket RefrigerationReplies: 14Last Post: 09-04-2006, 09:28 PM -
Searle cellar cooler control problem
By iceman007 in forum ElectricalReplies: 6Last Post: 06-07-2004, 08:57 PM -
New Capacity Control Solution
By embrown in forum New TechnologiesReplies: 19Last Post: 30-12-2003, 01:33 PM