Results 1 to 16 of 16

Thread: Oil carry over

  1. #1
    Join Date
    Aug 2012
    Location
    Dubai
    Posts
    3
    Rep Power
    0

    Oil carry over



    Gentlemen, A newly commissioned refrigeration plant , 10 nos HOWDEN screw compressors, 6 of them high stage 4 of them low stage cascade system, motor capaciy 630 kw HS and 200 kw LS, While compressor operating full capacity of HS compressor (above 70%) OIL carry over from oil seperator... one ltr per a minute..

    Refregerant R22

    Please advice, appreciate it



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Oil carry over

    Is just one of them doing it, or all? High or low stage?
    Is the plant operating within its design parameters?
    If it started immediately I would think the oil separator filters might not been installed properly.

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Oil carry over

    Possible HS compressors are over injecting oil, HS suction oversaturated and combined slide load rate too fast. And as NH3LVR suggested filters missing in separator.

  4. #4
    Join Date
    Aug 2012
    Location
    Dubai
    Posts
    3
    Rep Power
    0

    Re: Oil carry over

    Hi, NH3LVR, THANKS FOR YOUR COMMENTS, All HS are loosing oil very fast , one ltr /Hr. and while running 50% load oil not loosing. coalescers filter seems good , if it is damaged or not installed properly, it may happened even 50% running .
    Compressor Howden WRVI 255/193.

    Pla advise,

    Thanks,

    Joseph PUTEN

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Oil carry over

    What are the suction, intermediate and discharge pressures?
    Last edited by Segei; 09-08-2012 at 05:03 PM.

  6. #6
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Oil carry over

    Try to lower intermediate pressure. Go to 2.5 bar and then to 2.0 bar. Monitor operation and let us know how it goes. Your oil separators might be under sized. Lowering intermediate pressure will reduce mass flow and might improve oil carry over. Did you talk to Howden?

  7. #7
    Join Date
    Aug 2012
    Location
    Dubai
    Posts
    3
    Rep Power
    0

    Re: Oil carry over

    Hello Sir, Thanks for your comments, But if pressure drops up to 2.0 bar , intermediate temp wil be 14.5 deg C,
    That wil be effected of secondary refrigerant temp (Glyco)

    your comments will be validated

    Thanks,

    Joseph PUTEN

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Oil carry over

    Lync,
    For machines this size on R22 would expect at least 4 to 6 coalescers 225 dia x 1000mm.
    What do you have & what does contractor/supplier have to say?

    Do you know sealing design on end of filter ie "0" ring on ID or on end of filter?

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Oil carry over

    I beleive that the HS compressors are loading too fast, above 50% slide, the volumetric change and swept volume change is huge and separator velocities are huge, slow and easy load rates, system driven not load demand driven.

  10. #10
    Join Date
    Feb 2010
    Location
    new zealand
    Age
    42
    Posts
    67
    Rep Power
    15

    Re: Oil carry over

    I agree with ranger what coalescors are installed, also how are you measuring your 1L/Hr ? what is the discharge pressure and plant room temp? also why on earth is the system this size on R22? locate the designer and give him a kick from me.

  11. #11
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: Oil carry over

    Hi Lync
    Do the HS compressors have economiser lines fitted and if so do they have check valves installed?
    Paul

  12. #12
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Oil carry over

    Hi, all ...

    Quote Originally Posted by Nh34life View Post
    I agree with ranger what coalescors are installed, also how are you measuring your 1L/Hr ? what is the discharge pressure and plant room temp? also why on earth is the system this size on R22? locate the designer and give him a kick from me.
    ... a big kick from me too

    what is the reason .... probably, those units are custom made, quite cheap, without proper coalescer elements both in size and quality, installed maybe, without O-rings and not tightened, for sure undersized oil separators, because until 70% capacity without oil carryover .... what about oil recovery line installed and open or not? ... it is not easy to guess what went wrong .... let's wait for OP to put some more light on this ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  13. #13
    Join Date
    Sep 2004
    Location
    Germany
    Age
    79
    Posts
    4
    Rep Power
    0

    Re: Oil carry over

    First, how come that a system like this running with R22?
    Second, what kind of oil separator do we talk about?
    Third, probably the oil separator is calculated wrong and is to small for your system.
    You have to send me all technical information and a system drawing before it possible to give you an good advice.

    hortenllc@live.com

  14. #14
    Join Date
    Jun 2008
    Location
    Finland
    Age
    45
    Posts
    34
    Rep Power
    0

    Re: Oil carry over

    Hi

    Is there solenoid valves in oil injection lines?

    I had problem once with bitzer compressors losing too much oil, reason to this was leaking oil injection valve on standby comp and it blows all oil from separator through the compressor to the suction line and ended to pump separator (no check valve on suction, only discharge) when both comps was running there was no problems. And this was nh3 system

  15. #15
    Join Date
    Sep 2012
    Location
    India
    Posts
    77
    Rep Power
    13

    Re: Oil carry over

    Hi Lync

    Why not install seconday oil separator in series. Are the evaporators flooded design or dry expansion?

    Are the primary oil separators horizontal or vertical?

    In horizontal oil separators there are chances of higher oil carry over in case the oil charging is excessive.

    In case of vertical oil separators there should be enough space (Vertical separation space) in the oil separator for primary separation because of the change in direction, deflection, etc.

  16. #16
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Oil carry over

    What is the condensing pressure when the oil is being lost. I bet it is low enough that the CFM at the discharge is over loading the separator elements. Try raising the discharge pressure and see if this helps.

    Ken