    I just purchased an old True TSSU 48-12 Sandwich Prep table. It seems to cool just fine, but the evaporator fan seems to run all the time. It runs even when the cooling control is set to 0. The compressor comes on and off normally. Just wondered if this is normally the way these coolers operate?



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: True Prep Table question

    Evaporator fans normally run all the time unless the defrost system call for them to be off when in defrost.

    Yours is a chiller (as opposed to a freezer) so I'd expect natural defrost therefore fan on all the time. If in doubt check the wiring diagram if you can find it on the unit and trace where the fan signal comes from which may help confirm.

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: True Prep Table question

    .

    I agree with Andy.

    The fans run even when the comp is off and this
    prevents the coil from freezing.