    Hi guys
    I have been out off the hvac business for a while now but my brother asked me to
    add some r22 gas to his split unit so i tried to use the super heat method
    i did my measurments and this is what i got
    Outside Temp: 113F
    Inside Temp: 80F
    Target Superheat: 33
    Suctions pipe side Temp: 32F
    Suction side pressure converted to Temp: 21F
    Current Superheat: 13
    are my calculations right ??
    May 2008
    Farnham
    47
    Re: Superheat
    Naughty, you should not be using R22
    Oct 2008
    newbury
    1,444
    37
    Re: Superheat
    113 f in Sweden...Sound positively balmy
    michaelberg1138's Avatar
    michaelberg1138 Guest
    Re: Superheat
    This is probably a lot too late, but you have a major airflow problem. The evaporator will very quickly ice at those temps. Check the filter, blower and indoor coil for dirt, check that the registers are open, etc. Many techs think the adding refrigerant is the answer to every problem, usually ending up killing the compressor in the process.