04-08-2012, 12:38 AM #1
Can be mixed Sanyo GHP with ECOi?Oil for first is HP-9 and for the second is FV68S.
Doaes anyone have a viscosity chart?
04-08-2012, 01:40 AM #2
Re: Can be mixed Sanyo GHP with ECOi?Oil for first is HP-9 and for the second is FV6
No , THEY CANT BE MIXED.
Would you mix cake mix and engine oil??
04-08-2012, 10:18 AM #3
Well I know a system running in Germany for almoust 4 years without any problem sharing the same indoor units.Do you know if HP-9 have the same viscosity as FV68S cause i didnt find any spec for these oils. I want to know if this will operate on long terms since both are POE and by mixing them you get a new oil but how far is from the original characteristics on both oils?
04-08-2012, 10:19 AM #4
And HP-9 is the oil from the refrigerant circuit not the Nissan engine oil.
04-09-2012, 02:00 PM #5
HP9 GHP Compressor oil is
Kinetic: 13.7 cSt (@100°C)
Kinetic (40C): 78.6 cSt
FV68S Eco-i Compressor oil is
Kinetic: 8.31 cSt (@100°C)
Kinetic (40C): 69.6 cSt
Don't mix these systems Possibly In Germany one of the systems is a standby system and hasn't run or doesn't run very often. I can't say as we dodn't recommend this combination. panasonic will not support of help with this combination of systems.