    Varem Pressure Tanks



    Hi.

    Does anyone have experience on Varem Pressure Tanks?

    The tank is there to maintain constant pressure in the closed loop system. The tank will be installed after the pump, i.e. on the discharge line of the pump.

    They ask for the pressures, min & max pressures, in the catelogue. I am running a -4°C propylene glycol 25% at a flow of 5l/s. How do I know what my min & max pressures are?



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Varem Pressure Tanks

    It depends on where on the system the pumps and the plant is located...

    Our old physics tells us that for every 10 meters, the pressure will change 1Bar.
    Say that your plantroom is on the roof of a 20m tall building, then the minimum standing pressure will be 0Bar. However, if the plantroom is at ground level then the minimum standing pressure for the same system would be 2Bar.
    Same system just readings from different points...

    Now, to the minimum standing pressure above you will have to add a safety margin to ensure all sections of the system at all times are above atmospheric pressure, normally this would be 0.5-1Bar.
    Add to this the fact that you will need a pressure differential across the pump in order for it to move the water around, normally somewhere around 1Bar but it can be as little as 0.2Bar or as much as 6Bar.

    As you can see it all comes down to the design of your system, in my example above with a 20m building the answer to your question could be 0.5 to 0.7Bar or 2.5 to 3.5Bar both answers equally within "normal" values.



    .

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Varem Pressure Tanks


  4. #4
    Join Date
    May 2012
    Location
    South Africa
    Age
    36
    Posts
    15
    Rep Power
    0

    Re: Varem Pressure Tanks

    Thank you all.

    The layout is as follow: all the equiopment is on the rooftop and drops through the slab and runs hard agains the slap, lets say 0.5m

    The return line comes to the pump, on the discharge line the pressure vessel(with blader) and then the chiller. From the chiller it goes to the valve station witch is 2.5m below the slab.

    The valve station consists of the following: on the supply line is a ball valve, then goes trough a jacked vessel, on the return line is 2 ball valves and 3 way valve with by pass. Then the return goes back to the pump.


    Schematic.jpg

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Varem Pressure Tanks

    Try this sizing document, it may help....

    http://www.bssindustrial.co.uk/uploads/docs/323.pdf


    You pipeline sketch seems to show the 'expansion vessel' as a buffer tank with the flow passing through the vessel.

    Normally an expansion vessel is simply 'connected' to the system pipework via a 25 or 32mm pipe.
    Last edited by Brian_UK; 01-08-2012 at 11:35 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    May 2012
    Location
    South Africa
    Age
    36
    Posts
    15
    Rep Power
    0

    Re: Varem Pressure Tanks

    Yes I noticed I drew it wrong. It was something quick but I have changed it. Thank you