    Question Oil Temperature on CDHF Water Cooled CenTraVAc Chillers



    We been facing problems with sump oil temperaturs for the last one year. While the unit is offline the sump temp drops to 85 F from 120 F , The heater is working fine , we replaced the refrigerant pump seal but still the problem is presisting.What could be the problem is it something replated to the Oil Gas Seperator



  2. #2
    Join Date
    Jan 2010
    Location
    REPUBLIC OF SOUTH AFRICA
    Posts
    17
    Rep Power
    0
    Is the chiller using UCP2 or UCP3 or recent adaptive view. If its UCP3 with CH53O you will see that oil temperature setpoint changes when oil is about to reach setpoint setpoint goes high. Try to reload or upgrade to a latest version techview service tool software. I once had problem like that.

    Sent from my BlackBerry 9780 using Tapatalk

  3. #3
    a4anoop's Avatar
    a4anoop Guest

    Re: Oil Temperature on CDHF Water Cooled CenTraVAc Chillers

    Thanks for your reply ,will check and get back to you