    Insulating hot gas lines



    Hi Everyone,

    I was hoping you guys can help:

    Is it common to insulate hot gas lines in industrial NH3 systems? A little bit of back ground, +25F/85F
    NH3
    Liquid Recirc


    THANKS!



  2. #2
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Insulating hot gas lines

    It depends. Defrost hot gas line should be insulated. Hot gas line between compressors and condensers shouldn't.

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Insulating hot gas lines

    .

    It does depend on what the hot gas line is used for.

    Where is the hot gas going and will you still need it to be
    hot when it gets there?

    If you are using the hot has for defrost purposses or for
    heat recovery then it would be recomended to insulate the
    pipe, if the pipe is the discarge from the compressor to the
    condenser then usualy no, do not lag the pipes.

    Regards

    Rob

    .

  4. #4
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Insulating hot gas lines

    Insulating the discharge line is sometimes specified where there is a risk of burns.

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Insulating hot gas lines

    Quote Originally Posted by Mark View Post
    Insulating the discharge line is sometimes specified where there is a risk of burns.
    Thats correct and also if the condensers are remote to the
    compressor the discharge is insulated to prevent the
    discharge gas de-superheating before it gets to the condenser.

    Regards

    Rob

    .

  6. #6
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Insulating hot gas lines

    i don't think that desuperheating is bad. Actually, it helps to reduce heat rejection that required by the condenser. However, hot gas condensation in the discharge line is bad and insulation can help.

  7. #7
    Join Date
    Mar 2010
    Location
    usa
    Age
    46
    Posts
    120
    Rep Power
    17

    Re: Insulating hot gas lines

    Defrost lines with the chance of condensing refrigerant should be to prevent Shock when a defrost started.