    carrier hs090 air cooled chiller



    Hey guys, im new and need some help if possible. when the compressors come on the pump motor starter kicks out and the chiller shuts down on low flow alarm. the motor starter is in auto position. i have burnt out two chilled water pumps already. not cheap!! any help would be appreciated. thnx.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: carrier hs090 air cooled chiller

    Don't recognise the model number, any other data plates about?

    If you have good pump starters and overloads why are the pumps getting burnt out?

    It seems that you may have a voltage supply problem and the compressor starting up is dropping the voltage below safe levels.
    Brian - Newton Abbot, Devon, UK