25-07-2012, 07:19 AM #1
Unit with suction accumulator and witout oil separator
Hi all.
I have condensing unit on semihermetic reciprocated compressor. It will work on freezing room, evaporating temperature -27C, suction pipe is very shot. I need to use suction accumulator because unit will use for frezzing, I think that oil separator also needs becaurse there will be low evaporating temperature. Am I right or oil separator may be not nessesary?In some places will have to think ...
31-07-2012, 12:50 PM #2
Re: Unit with suction accumulator and witout oil separator
1) It is better to use oil separator since the evap temp is -27 deg c ........better to keep oil off the evaporator than loose the capacity .
As much as low oil in evaporator , it helps to better the system efficiency.
2) accumulator would be of help since after defrost cycle termination, there is a possibility of liquid carry-over .........
02-08-2012, 07:55 AM #3
Does oil separetor need if in system (low or medium temperature) there is suction accumulator or not?