    Chiller condenser pressure high at start-up



    Dear forum fellow we have a TRANE electric chiller with screw compressors.
    In the morning when we start it,condenser pressure goes high and usually this compressor offers two trips before it gets stable .
    Cooling tower is functioning well ,might be condenser tubes problem.
    Please share your experience and guidance here.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,713
    Rep Power
    46

    Re: Chiller condenser pressure high at start-up

    Hi pakblogger.
    A bit more info would help.
    If the system is on Ammonia then when did you last purge from the condenser?
    As you mention the condensing tubes, whats the state of your tube jets (if fitted?)
    You say in one breath the cooling tower is functioning well but then it may be the tubes!

    Slightly confusing, can you elaborate more?
    Grizzly
    Just guessing at this stage.

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Chiller condenser pressure high at start-up

    Don't forget to check the basics first - strainer on pump. Is there a vsd & water in/out temps would be helpful as would hp & refrigerant as Grizzly said.

  4. #4
    Join Date
    Jun 2012
    Location
    Pakistan
    Posts
    44
    Rep Power
    0

    Re: Chiller condenser pressure high at start-up

    Thanks for reply.
    It is dual circuit compression chiller without tube jets.
    We recently serviced strainers of all cooling water pumps.
    Last year we cleaned condenser tubes with hydro jetting process.
    We dont see any abnormality in cooling tower operation and its related temperatures.
    I suspect the state of condenser tubes.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chiller condenser pressure high at start-up

    Is there any water treatment regime being used on the condenser water system?

    What are the water condtion test results showing?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Chiller condenser pressure high at start-up

    Possibly screw compressor is loading too fast with high startup loading. Condenser water flow rates too low, or too high can have same effect. Non condensibles in system.

  7. #7
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: Chiller condenser pressure high at start-up

    that model of machine is? type of refrigerant?

  8. #8
    Join Date
    Jun 2012
    Location
    Pakistan
    Posts
    44
    Rep Power
    0

    Re: Chiller condenser pressure high at start-up

    I thank all of you fellows.
    Chiller is of TRANE company,RTWA-216 and refrigerant is R22.Make-up for cooling water is done from underground water taken out with deep well turbine pump.Arcoburag chemicals are used on cooling water side to maintain chemistry.
    Yesterday again ,strainers have been cleaned ,cooling water flow rate adjusted and little improvement in condenser pressure condition has been observed today .
    However we intend to clean condenser tubes but it is not possible to take it out of service right now as operation of chiller is required now a days.

  9. #9
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Chiller condenser pressure high at start-up

    Hi
    i would go with magoo!!
    all other problems would lead to a permanent state of high pressure,but the unit would start! but if your machine is loading to fast ,or your pump isnt pumping enough water this would fit perfectly !!,
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  10. #10
    Join Date
    Jun 2012
    Location
    Pakistan
    Posts
    44
    Rep Power
    0

    Re: Chiller condenser pressure high at start-up

    Thank you all .

    Really this is very good forum to get guidance from you people.
    matter stands partially solved now.
    For future I want your guidance related to tube cleaning of condensers.
    These are copper tubes and as I said we intend to clean these tubes in near future,kindly may I know your expertise regarding different methods of tube cleaning and their effectiveness.

  11. #11
    Join Date
    Jun 2012
    Location
    Pakistan
    Posts
    44
    Rep Power
    0

    Re: Chiller condenser pressure high at start-up

    Or should I start a new thread for getting your guidance related to different methods of tube cleaning and their effectiveness ?

  12. #12
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15

    Re: Chiller condenser pressure high at start-up

    approach measures the condenser, check the temperature sensor indicating the saturated condensser is correct, measures pressure compressor discharge pressure gauges

  13. #13
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Chiller condenser pressure high at start-up

    Yes pakblogger you should start a new thread for the best results, but first search - all the answers may already be there.

  14. #14
    Join Date
    Jun 2012
    Location
    Pakistan
    Posts
    44
    Rep Power
    0

    Re: Chiller condenser pressure high at start-up

    Thanks all posters.

  15. #15
    Join Date
    Jan 2010
    Location
    REPUBLIC OF SOUTH AFRICA
    Posts
    17
    Rep Power
    0
    What model of that Trane Chiller?


    Sent from my BlackBerry 9780 using Tapatalk

  16. #16
    Join Date
    Oct 2007
    Location
    Northamptonshire
    Age
    60
    Posts
    25
    Rep Power
    0

    Re: Chiller condenser pressure high at start-up

    Check start up current against second circuit as it is possible the screw's slide has siezed and it is trying to start fully loaded (had this myself)

  17. #17
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    78
    Rep Power
    13

    Re: Chiller condenser pressure high at start-up

    I think we need to clean the condenser, and check the refrigerant charge.
    hello

  18. #18
    Join Date
    Feb 2008
    Location
    sydney
    Age
    52
    Posts
    32
    Rep Power
    0

    Re: Chiller condenser pressure high at start-up

    does it have condenser water bypass?