    Mitsubishi 2502 Fault on City Multi System



    I have an R407c City Multi system running 4 indoor units (PLFY-P63VKM-A). I have a fault code 002 2502 (Drain pump fault). None of the units are labeled up. Is there anyway i can find out which indoor unit is at fault. None of them have any water leaks on yet but i understand that 2502 can mean the water level is higher than normal and the drain pan or drain outlet could be blocked. Thanks







  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Mitsubishi 2502 Fault on City Multi System

    pull the drain plugs on each indoor-it will be the one with the most water in

  3. #3
    Join Date
    Nov 2009
    Location
    Here there Everywhere
    Age
    51
    Posts
    8
    Rep Power
    0

    Re: Mitsubishi 2502 Fault on City Multi System

    The units units are laid out in a square, i guessed at which was unit two was and did get maybe a 6th of a large bucket of condensate out it. I'm going back tommorow to drop the tray as ive found the sites maintenance over the past few years has been poor. I'm expecting to find a tray and pump full of crap. I'm surprised you cant interpret the controller though

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Mitsubishi 2502 Fault on City Multi System

    u can on a par f 27- hit check button twice quicky with the unit turned off and will show the address- unless u got 1 remote and 4 indoors- check the indoor pcbs for the address. chances are theyre all gonna be ****ted up and want cleaning- prob evap coils will want blasting out too

  5. #5
    Join Date
    Mar 2011
    Location
    Singapore
    Posts
    212
    Rep Power
    16

    Re: Mitsubishi 2502 Fault on City Multi System

    002 is indoor unit and 2502 is the pump issue or float switch or indoor controller board trouble.
    You can press check button twice from remote controller to see the indoor unit address. (follow IM's instructions)
    However so many time resets (On and Off with 2502 error) will lock the entire system and you can't able to run the system. All the local remote controllers will blink.
    Note: Most cases, 2502 occurs due to drainage pipe choke. Or jelly stuck in the pump.

  6. #6
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,120
    Rep Power
    25

    Re: Mitsubishi 2502 Fault on City Multi System

    It'll be the unit with the rotary switches set 02.
    Or if one controller delete 1,3,4 of it and 2 is the only one left...
    Cheers
    Stu