Results 1 to 10 of 10
    Sep 2006
    Turkiye
    48
    Ice on evaporator
    We manufactured a refrigerated service case, with an evaporator who has fans. Our customer is using it for selling meat . And refrigerator must work at -3 degrees . And it causes ice on refrigeration. I made natural defrost 10 minutes every hour but it didnot solve the problem. So i used heaters to melt the ice. Do you have any experiences and solutions about this problem. Thamkyou
    Oct 2008
    newbury
    1,444
    Re: Ice on evaporator
    If the room is to be -3 how do you expect the ice to melt below freezing/
    Yes the evaparator unit should be able to be fitted with heater kit. Contact supplier of evaparator and order it plus you may need new controller/ panel and additional wiring to suit.
    Oct 2008
    newbury
    1,444
    double post...
    Sep 2006
    Turkiye
    48
    it is not a room. it is a refrigerated service case. for selling meat.
    May 2012
    59
    1,528
    With meat also check the evaporating temperature of the refrigerant.
    If it is too low it will cause complications. Normal evaporators
    have about a ten degree differance over the coil but if you do
    this to fresh meat it can cause the meat to dry out, so the
    temp diff needs to be less.
    If it is a display case then it will defrost naturaly but if it
    is a cold room then it will need heat added to defrost.
    If it is a display then set the defrost for about 30 to 40 mins
    every four to six hours. But now you have put heaters in they
    will require less time.
    Rob
    Sep 2006
    Turkiye
    48
    thankyou Rob
    May 2012
    59
    1,528
    Quote Originally Posted by napter38 View Post
    thankyou Rob
    Your welcome.
    Oh by the way it is very common for manufacturers to run
    meat cases, deli, dairy and such like (air off down to
    about -5 deg C) with off cycle defrost and you were correct
    in the first but you did not allow enough time for the defros
    to happen.
    Remember if the coil is iced up as the air flow passes over the
    coil and defrosts it the air off the evap is still suficiantly low
    so that there is no noticable differance in case temp.
    That is why off cycle defrost needs to be for a longer time
    and times of 45 mins are not unusual......
    Rob
    Sep 2006
    Turkiye
    48
    we were using digital thermostat with one prob. I will change it with the thermostat which has two probs. Refrigerator will make defrost untill evaporator prob temp. is +8 deegrees
    May 2012
    59
    1,528
    Yes, the best way is with two probes.
    Rob
    Oct 2003
    5,630
    Or even better, use hotgas defrost.
Tags for this Thread
