    New electronic leak detector .



    So i have a electronic leak detector . Which sniffs out all refrigerants i use.
    This is handy for when the system already has gas in it.
    When its empty and has a small leak i need to charge it with 10% refrigerant and then pump nitro in the rest.

    Gas prices have risen 300% in Australia so wasting gas like this is not the best idea.
    Is there a way with out using an ultrasonic leak detector that i can sniff out just nitro .
    Also how much refrigerant is need to be picked up in thinking 10% is abit to much ?

    Would this device pick up nitro ?

    http://www.interscience.be/promoties...akdetector.pdf



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: New electronic leak detector .

    leakspray will pick up 100% nitro-no need for ur 10% of refrigerant

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: New electronic leak detector .

    Hi Simon
    I use (allegedly) R22 for trace, pump it up to 10psi then in staged pressures with nitro in the past. I read this measure in a reference to ASHRAE guidelines. But the young apprentices say they are taught there should be enough trace gas in the oil which will mix with nitro, but I'm not so sure as these younger ones have more problems finding leaks. If working on an R410a system I would use the R410A as trace gas as the molecules are smaller then R22. How ever I am sure we need to reclaim this mix of gases so as not to break the rules. I re-did the refrigerant section at tafe last year and the rules are a little grey as it focuses on other methods of tracing gas leaks. I just checked and it says
    Except where used as trace gas (see 3.2.2), flourocarbon refrigerant must not be used for the purpose of leak testing.
    May be used by manufacturers
    a must be premixed not greater than 10% by volume.
    b must be recovered
    c must be pretested for gross leaks with non flourocarbon method.

  4. #4
    Join Date
    Dec 2011
    Location
    Australia
    Posts
    69
    Rep Power
    13

    Re: New electronic leak detector .

    Thanks for your detailed reply telsa .

    The problem is that i dont want to use gas because it cost money and then time to recover the gas . nitro fills up reclaim bottle pretty fast.

    My apprentice said there is a mix new project that is a special kind of nitro and then you buy a special kind of sniffer and you can use it the same as normal . since he is dum and cant explain things probably all use correct names i dont know where i can find this new way of sniffing with no refrigerant .

  5. #5
    Join Date
    Jan 2012
    Location
    New Zealand
    Age
    55
    Posts
    7
    Rep Power
    0

    Re: New electronic leak detector .

    try looking for an ultrasonic leak detector these can find leaks where any pressure is present so require no refrigerant at all and also are able to source leaks where background refrigerant is present

  6. #6
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: New electronic leak detector .

    You can use a nitrogen/hydrogen mix, which needs a lower pressure than OFN for leak testing and does not require any refrigerant. Downside is that you need a special electronic sniffer and the 5% hydrogen/nitrogen mix is quite expensive and only available form a few specilaised supliers. It will normally find smaller leaks when other methods sometimes fail.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: New electronic leak detector .

    .

    Unless the system is totaly empty which they very rarely are
    there will always be enough gas inside the system to find a leak.

    Bear in mind those electronic leak detectors are sensative down to
    between 3 and 5 PPM. That means a gas leak of between 3 and 5
    grams a year. Think about it 3 to 5 grams a year is such a small leak.

    Now I'm not sure about Australia but in Europe we can't add gas to
    leak test, it goes against our F-Gas directive....

    In the UK we have a trace gas that uses nitrogen and Hydrogen and
    then a leak detector to find the gas, but it is as expensive as buying
    a good Ultrasound leak detector...

    Regards

    Rob

    .
    Last edited by Rob White; 24-07-2012 at 02:49 PM.

  8. #8
    Join Date
    Jul 2008
    Location
    Turkey
    Posts
    6
    Rep Power
    0

    Re: New electronic leak detector .

    There are some paints produced by Refco called Glo-Leak, you just mix it in oil before adding gas -any gas- or inject it with a special gun to the system, and it does not effect the coolant performance. Under UV light and some special glasses -I'm not sure if they're special, might be just some kind of filter- you can even find microscopic leaks they say, haven't tried it myself, I'm using Würth's leak detection sprays, which I find very effective and cheap -~15US$ / bottle-. You can check REFCO's 2012 catalog chapter 6, pages 86-87 for glo-leak.

  9. #9
    Join Date
    Dec 2011
    Location
    Australia
    Posts
    69
    Rep Power
    13

    Re: New electronic leak detector .

    you dont even need glasses most of the time or a uv light for that glo-leak .

    Its still not illegal because you try to find the leak first with nitro and bubbles and its to small to find . then you fill it with a tiny bit of gas then you find the leak after 30mins max reclaim all that gas into a bottle. you would loose less than a purge of a gas line.

  10. #10
    Join Date
    May 2001
    Location
    North Wales
    Posts
    47
    Rep Power
    0

    Re: New electronic leak detector .

    ultrasonic leak detectors are they any good???
    what sort of experience have engineers had so far with them any good... worth the mony...etc.
    Any reply s on this matter please would be good.

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: New electronic leak detector .

    Quote Originally Posted by Gwyn View Post
    ultrasonic leak detectors are they any good???
    what sort of experience have engineers had so far with them any good... worth the mony...etc.
    Any reply s on this matter please would be good.
    Don't use one now but have used them in the past.

    Found leaks every time regardless of the background noise levels. I would recommend them as 'another' tool to have in the box.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    May 2001
    Location
    North Wales
    Posts
    47
    Rep Power
    0

    Re: New electronic leak detector .

    Quote Originally Posted by Brian_UK View Post
    Don't use one now but have used them in the past.

    Found leaks every time regardless of the background noise levels. I would recommend them as 'another' tool to have in the box.
    Great will have to start to look into getting one then any good preferences as to make model etc?

  13. #13
    Join Date
    Sep 2012
    Location
    the Netherlands
    Posts
    2
    Rep Power
    0

    Re: New electronic leak detector .

    Hi all,

    It appears in this thread a lot of knowledge of leak detecting is present and I would like to make use of that.

    I am looking for a stationary leak detector located on a R134a installation. This detector should not react to N2 (nitrogen gas).

    Does anyone know which sort, brand, type, etc. I can use?


    Kind regards,

    JR